UFH Manifold Issues - Reverse flow?

The UFH pump does the heavy lifting. If a UFH system is outputting say 5.0kW with UFH flow/return of 35C/28C from a boiler with a flowtemp of 60C, the UFH circ rate is 10.24LPM but the boiler's is only, ((35-28)/(60-28)*10.24, 2.24LPM or less than 22%.
On UFH systems fed by an ASHP where there are no rads fitted (ie all UFH in the house), then the UFH circulator is not usually required, the main circulator doing all zones as the water does not need mixing down to a lower temperature as it does on systems that use a combination of UFH and rads on >60C water temperatures.
 
The only interaction I've noticed between the CH and UFH is that when both systems are calling for heat, the UFH will barely work - wondering if it's because the UFH flow is dependent on the main boiler supply rather than the UFH circulating pump, and the boiler can't keep up.
No, I'll say it for the third time. It doesn't work because that UFH pump is installed the wrong way round.
 
No, I'll say it for the third time. It doesn't work because that UFH pump is installed the wrong way round.
Yes, understood - I was answering the other poster's question about whether there was a zone valve.

In doing so, I was just highlighting that the current setup does "work" to an extent, but seemingly with the flow in reverse because of the issue with the pump (as you've confirmed), and only when the CH isn't also on.

Thanks for the info, I'll get the pump corrected asap.
 
No idea who installed it, its a Ivar manifold.
It might be used with OIl Fired Boilers? which don't recommend a return temperature below 40C, the above UFH returns some of the mixed (UFH inlet) water to the boiler which will be say 7C to 10C higher than returning some of the UFH outlet water.
 
Last edited:
Hi all,

Looking for some advice on my UFH, which was installed during a renovation 2 years ago. It's never worked particularly well, taking hours to warm up and sometimes not reaching temperature at all on colder days.

It's a 4-loop system with a Wilo pump and mixing valve, sharing a boiler with the radiators.

I've been trying to figure out what's going on and noticed a few things:

- Flow meters show 1–2 L/min when the boiler fires, but gradually drop to zero when it stops, even though the UFH pump is still running and the thermostat is calling for heat.

- Increasing the pump power actually seems to reduce the flow, sometimes to zero. Switching to constant-pressure mode (setting 2) has helped a bit.

- Turning the mixing valve up to 60–65c gives me consistent flow, but dropping it back to 45c causes it to stop again. Obviously don't want to run it that hot with engineered wood flooring.

- The bottom manifold heats up before the top one (which has the flow meters). Shouldn't this be the other way around?

- It also seems to struggle more when the radiators are on.

The thing I'm most suspicious about is that the arrow on the Wilo pump points downwards, towards the bottom manifold.Is that correct for this setup? Could the water be circulating backwards through the manifold?

I'm wondering whether the boiler pump is doing most of the work, which might explain why the flow stops when the boiler stops firing, and why turning up the UFH pump seems to make things worse.

I spoke to an engineer who basically said that if the room eventually gets warm, he'd leave it alone. But it's been rubbish since installation and I'm worried something isn't right. Also don't want there be damage from incorrect flow.

Interested in people's thoughts. (I've watched about as much YouTube plumbing content as I can manage...)
View attachment 426598

Is that RH side marked R on the TMV blanked off as it should be if its the Reliance SKU: HEAT 970366 type of TMV which can be mounted to the left hand or right hand side of the manifold and if so, where is the cold return to the boiler teed off?. The hot from the boiler should go to the bottom port if of the reliance type.
Edit: If its the latest type then, LH port is UFH return, RH port (R) is the cold return to the boiler, bottom port is HW inlet from the boiler and top port suppliesies mixed flow temperature water to the pump.

1794873519603.png
 
Last edited: