Despite saying I wouldn't do any further work until Monday, curiosity got the better of me.Thanks everyone for your suggestions. Lots for ne to try, plus a replacement blender valve has arrived. She who must be obeyed has decreed no more UFH work until Monday. I'll provide an update on progress next week
From the responses received I did the following.
Setting the blender to minimum I could hear the blender doing its work. Set midway the flow rates on the loops were correct. Set to minimum they dropped.
With the blender set midway when I switched on the radiator zone the flow rates on the loops dropped.
It seemed that if the pressure dropped i.e blender working or the radiator zone operating, then the flow rate on the loops dropped.
I looked at the pump Wilo-para ma

nual but to be honest I don't really understand it. It was set as in picture 2(2 leds diag) . I think this variable differential pressure. I cycled through the settings until the pressures didn't drop see picture 2 (3 leds in row) I think this is constant speed. Everything seemed to be working OK. Blender set to minimum water temperature not going above 35 loop pressures maintained. You can hear the pump so not sure I have got the correct settings.I'll contact Wunda on Monday and see what the pump should be set to.