Upgrading Garage Electrics

Joined
1 Nov 2006
Messages
202
Reaction score
2
Location
Lancashire
Country
United Kingdom
Hello everyone and seasons greetings to you all .

My garage has just one 13A socket , which I think , is tee`d off the ring main using a single 2.5 cable . A fused spur is connected to this for the light switch.

Running into this I have a freezer , a tumble dyer , a pond UV light and a small dosing pump for my pond .

I`m about to add an air source heat pump for the pond , which is `plug and play` rather than hard wired . It draws a maximum of 1kw of power .

If I use my socket as it is , will I be overloading it ?

If so , what do I need to do to increase my capacity ? I`d like a rough idea of the work involved , before I call in a professional . My meter is at the opposite side of the house , so running cables might be an issue ? If so , I might run the cable for the heat pump to another indoor socket .

What do you think ? Any advice would be much appreciated .
 
1kW - 4A - is fine in a 13A socket.

However, I am confused how the freezer, tumble drier and pump "run into this"; what does that mean?
 
If the tumble dryer and heat pump don’t run at the same time it should be fine. Is the garage on a fused spur? If not you‘d probably be able to run both at the same time.
 
If the tumble dryer and heat pump don’t run at the same time it should be fine. Is the garage on a fused spur? If not you‘d probably be able to run both at the same time.
There is a fused switch attached for the light , but there are no other fuses on the cable . I just had a look at the dryer label and it uses 2200w . Yes , I could make sure they`re not run together , but might be better if I can route the heater to another socket , perhaps ?
 
I take it the socket is in fact a double socket despite "My garage has just one 13A socket".

If that is the case and the cable is 2.5mm² then you could run the items at the same time.
3200W is 13.33A so will be fine on a double socket.

You cannot fit any more sockets on an unfused spur; i.e. the cable, not a misnamed Fused Connector Unit.
 
I take it the socket is in fact a double socket despite "My garage has just one 13A socket".

If that is the case and the cable is 2.5mm² then you could run the items at the same time.
3200W is 13.33A so will be fine on a double socket.

You cannot fit any more sockets on an unfused spur; i.e. the cable, not a misnamed Fused Connector Unit.
No , it's a single socket . I have a 4 gang extension plugged into it via an RCD . The 4 appliances mentioned in my original post are plugged into it.
 