Vaillant 242 Turbomax hot water intermittent

Discussion in 'Plumbing and Central Heating' started by primetime, 16 Jul 2016.

  1. primetime

    primetime

    Joined:
    20 May 2013
    Messages:
    95
    Thanks Received:
    2
    Location:
    Bristol
    Country:
    United Kingdom
    The hot water for the shower doesn't always come on but is ok for the other hot water taps - basin and kitchen sink. The shower has the lowest flow rate.
    I suspected the diverter valve diaphragm but there were no splits or tears. I replaced the diaphragm and everything else that came in the diverter service kit. The hot water seemed ok for a few days but has gone back to being intermittent.
    The microswitch doesn't seem to operate the times the DHW doesn't come on despite re-adjustment.
    The Central Heating radiator supply pipe also gets warm for a little way (heating not on) when the DHW runs for a little while.
    Replacement of entire diverter required?
     
  2. hertsboilers

    hertsboilers

    Joined:
    26 Nov 2011
    Messages:
    2,585
    Thanks Received:
    962
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    Yes, whole valve time.
     
  3. Bunnyman

    Bunnyman

    Joined:
    22 Mar 2010
    Messages:
    5,489
    Thanks Received:
    1,839
    Location:
    Northamptonshire
    Country:
    United Kingdom
    Yes 011289 is what u need
     
  4. primetime

    primetime

    Joined:
    20 May 2013
    Messages:
    95
    Thanks Received:
    2
    Location:
    Bristol
    Country:
    United Kingdom
    Thanks. I had another go at adjusting the microswitch. Seems ok for now.
     
  5. hertsboilers

    hertsboilers

    Joined:
    26 Nov 2011
    Messages:
    2,585
    Thanks Received:
    962
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    So you will still get warm radiators when you fill your bath.
     
  6. Sponsored Links
  7. primetime

    primetime

    Joined:
    20 May 2013
    Messages:
    95
    Thanks Received:
    2
    Location:
    Bristol
    Country:
    United Kingdom
    Rads not getting warm, just a short section of the supply from the diverter.
     
    • Like Like x 1
  8. Bunnyman

    Bunnyman

    Joined:
    22 Mar 2010
    Messages:
    5,489
    Thanks Received:
    1,839
    Location:
    Northamptonshire
    Country:
    United Kingdom
    Well you asked for advice mate, just change the valve, i know its expensive but u will do the same as many professionals, fanny around convincing urself it seems ok, the problem is there
     
    • Like Like x 1
  9. primetime

    primetime

    Joined:
    20 May 2013
    Messages:
    95
    Thanks Received:
    2
    Location:
    Bristol
    Country:
    United Kingdom
    I appreciate the advice. I got to the same conclusion but wanted to hear it from someone with more experience or if there something else that could be done. Not saying I won't replace it but in no rush just yet. Have sourced a new diverter assembly. Thanks again.
     
    • Like Like x 2
  10. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    63,560
    Thanks Received:
    4,512
    Location:
    London
    Country:
    United Kingdom
    I have successfully adjusted the switch in a few cases. But I also agree that on that model its better replacing the whole valve.

    Tony
     
  11. AGAS

    AGAS

    Joined:
    21 Feb 2014
    Messages:
    9,692
    Thanks Received:
    1,706
    Location:
    down south
    Country:
    United Kingdom
    don't be like some wally's on here who don't take the advice from someone who knows what their talking about with vaillants ( bunnyman ) , because if you go the cheap way you will only spend ( cost & money ) much more in the end .

    there are plenty of examples on this forum
     
  12. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Sponsored Links
Loading...

Share This Page