Vaillant/Heatmiser wiring problem

Discussion in 'Plumbing and Central Heating' started by sw2newbie, 6 Sep 2016.

  1. sw2newbie

    sw2newbie

    Joined:
    22 Jun 2011
    Messages:
    5
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    I have a Vaillant ecoTEC plus 630 system boiler supplying 4 central heating zones (3 radiator and one wet underfloor) and one unvented hot water cylinder. The system is controlled by a Heatmiser wiring centre linked wirelessly to 4 room thermostats/timers.

    When the heating is on and the hot water timer is on too, hot water is produced. However, when the heating is off (as has been the case over the summer), there is no hot water.

    I have checked the zone valve for the boiler and it is working (and as I understand it, if it wasn't working, there would be no hot water even with the heating on because there would be no way for hot water to flow into the cylinder). The timer for the hot water is also communicating correctly with the wiring centre. The wiring in the wiring centre has also been connected according to the instructions.

    I therefore think that the problem lies with the wiring centre not being connected to the boiler correctly, such that there is no call for heat when the hot water valve operates independently of the heating valves, and it is only the heating valves that operate the call for heat on the boiler.

    Is there a simple fix for this? I have not yet taken the boiler apart to find the connections made by the heating installer, but from the instruction manual it seems as though there are a lot of terminals.
     
    • Like Like x 1
  2. Sponsored Links
  3. Dan Robinson

    Dan Robinson

    Joined:
    1 Jul 2007
    Messages:
    56,034
    Thanks Received:
    9,420
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    Why take the boiler apart? Its working.
     
    • Like Like x 1
  4. sw2newbie

    sw2newbie

    Joined:
    22 Jun 2011
    Messages:
    5
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    I meant take the casing off to find the wiring terminals to see if there's an issue with how the wiring centre has been connected. I wasn't planning to strip it down and throw parts all over the kitchen floor.
     
  5. Dan Robinson

    Dan Robinson

    Joined:
    1 Jul 2007
    Messages:
    56,034
    Thanks Received:
    9,420
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    But it's working!!!
     
    • Like Like x 1
  6. sw2newbie

    sw2newbie

    Joined:
    22 Jun 2011
    Messages:
    5
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    OK. Fine. So what is the likely source of the problem? Why would there be a call for heat from the central heating zone valves but not from the hot water cylinder valve, when both are wired into the wiring centre according to the instructions?
     
  7. Sponsored Links
  8. Steelmasons

    Steelmasons

    Joined:
    10 Oct 2011
    Messages:
    16,396
    Thanks Received:
    3,969
    Country:
    United Kingdom
    Have you checked for 240 volt @ orange core of HW zone valve when a call for heat (end switch)?
    Possibly HW zone valve has been manually opened due to faulty motor?
    Could be a number of issues which would take all of 5 minutes to diagnose if you know what you're doing.
    For what reason would you want to remove boiler front cover?
     
    • Like Like x 1
  9. Dan Robinson

    Dan Robinson

    Joined:
    1 Jul 2007
    Messages:
    56,034
    Thanks Received:
    9,420
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    A please and a thank you might not go amiss too.
     
    Last edited: 6 Sep 2016
    • Like Like x 1
  10. Steelmasons

    Steelmasons

    Joined:
    10 Oct 2011
    Messages:
    16,396
    Thanks Received:
    3,969
    Country:
    United Kingdom
    Hey Dan , I'm not sure that the OP understands you when you say the boiler is working..:ROFLMAO:;)
     
    • Like Like x 1
  11. AGAS

    AGAS

    Joined:
    21 Feb 2014
    Messages:
    9,695
    Thanks Received:
    1,718
    Location:
    down south
    Country:
    United Kingdom
    if the boiler has been working OP why are you considering the wiring is wrong ( as dan is saying ) ?? think you better get someone in before opening that boiler up :cautious:
     
  12. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page