DHW heat exchanger changed. No difference.
I'm still a bit baffled by the fact that I'm only burning half the gas I should.
hanks gasguru. It took 76 sec per revolution which works out as 14.36. Should it be running at approximately 24? Gas pressure problem?
I have the same bolier and when I had lukewarm hot water one revolution of the gas test gauge on the meter was taking 49secs which gave a gas consumption of 22.28kw.
When it was fixed (control board issue) one revolution was taking 38 secs giving a consumption of 28.73kw and toasty hot water.
Now my gas flame was not increasing in size but yours is so could it be something as simple as a blockage in your gas section and not enough gas getting to burner.
Might be worth timing flow again to make sure 76 secs is correct.