I'm new to all this but can anyone possible tell me, When setting up the CH on for the various times zones on the VRT... do you also need to set the pump to run..

Hope this makes sense...

at the moment I've set the CH to come on and the Pump at the same time; Is this correct or does the pump automatically come on.

Cheers
 
Sponsored Links
I have a ecotec 937 controlled by the vrc430 - i just set the times for central heating and thats it - pump is automatic.

Shady
 
Hi

The 'pump' setting on the 360 refers to an auxiliary pump, not the actual boiler pump. Its meant to control a secondary hot water pump for use with a cylinder or a large system pump with a low loss header etc.

As the last post says, just set your heating times and the boiler pump will look after itself.
 
Sponsored Links
Thanks "the 831bunny" and "Shadybrady" Much appreciated... I'll go reset tonight.