That looks good in the theory book, but have you actually ever achieved this in real life?... but the radiator temperatures will be lower - flow 72°C return 52°C.
But say you only need a 20kW boiler and have 38kW rads. Then the temperatures would be 61°C and 42°C.
None of which where solely, or even predominantly due to not being range rated, but caused by poor installation/maintenance.And there have been several topics about OPs with problems when the heating output of a combi boiler has not been range rated.This of course assumes that it is:
A, a conventional boiler,
That looks good in the theorybooks, but have you ever achieved these figures in real life?The second (C) is easy to determine as the heat required is proportional to the outside temperature. If you need 22kw to raise the temperature from -1°C to 21°C then you will need 11kw to raise the temp from 10°C to 21°C and 5kW to raise the temp from 16°C to 21°C.B, the smaller boiler will have a lower minimum rate than the bigger model,
C, that the house will actually need less than the minimum rate of the boiler,
Item B can be resolved by checking the manufacturers specifications and selecting the most appropriate boiler - though installer's preferences may distort this.
The client will have no clue about what that all actually means, nor what is realistic; it is the designer's job to do that for him.Then you discuss this with the client and get him to agree what temperatures to use.D, it will never get colder than the design temperature outside,
That sounds fine on paper, but in real life, it is not that easy as very few people are clairvoyant. Discussing future needs is one of the first things I do, and fewer than 1 in 5 is sure there will not be any extensions or alterations.You install a system to meet the current residents requirements, not some hypothetical future requirement.E, the occupant is not, and never will be, Jamaican and likes the house warmer than the standard design temperature,
And another case where 4 out of 5 are not sure.Another case where you discuss this with the client before making your recommendation.F, at not time in the future will there be an extension built, a loft converted, or any other need for more output,
There might be a minute loss in theory.Loss of unburnt gas prior to ignition every time the boiler comes on?G, that it is actually a demonstrable disadvantage to have the boiler cycling during some periods, rather than a theoretical issue,
Even at a cycling speed of only 5 minutes, you would be looking at something like 0.00001 cubic metre per day, IF the boiler had such a poor performance that gas would be out of the flue before ignition; less than one single pound over the lifespan of the boiler.
This reminds me of the early days of central heating when the sales pitch was "guaranteed temperatures". This was achieved by oversizing everything. Fine when gas was cheap and the problem of global warming had not appeared over the horizon.H, the owner believes that the demonstrable comfort of over capacity does not outweigh the theoretical downside of cycling.
It seems you have reached the heart of the problem: your ideas are based on common believes held some 30 years ago.
Oversized rads actually make modern boilers more efficient.
Contrary to 30 years ago, boilers modulate, reducing the cycle rate by a factor 10, if not more.
The issues using more gas and global warming are totally irrelevant for a number of reasons:
A slightly oversized modulating premix boiler does not use noticeably more gas than one that is "exactly" sized.
There is no evidence whatsoever that global warming is still happening; a sharp dip started in the second halve of the nineties.
Even if global warming were still happening, there are only vague theories that it is anthropogenic, and 3 very strong indications that it is not.
Even if there was a measurable increase in gasuse of an oversized boiler, it if absolutely negligible in terms of total national/global use.