vokera linea 24 ,too much pressure ?

  • Thread starter Thread starter ezz
  • Start date Start date

ezz

Joined
31 Dec 2007
Messages
16
Reaction score
0
Location
Lincolnshire
Country
United Kingdom
hi, had some problems with my vokera linea 24,changed my prv everything fine,except when running pressure is going up to 3 bar or close to it,set pressure to just over 1 bar in first place,heating comes on water nice and hot,just wondered if air in expansion vessel needs topping up. thanks
 
use a drain point - not the PRV, these very often do not reseal after opening so then need replacing.
 
there should be something looking like this

<a href="http://s260.photobucket.com/albums/ii30/twgas/?action=view&current=draincock.jpg" target="_blank"><img src="http://i260.photobucket.com/albums/ii30/twgas/draincock.jpg" border="0" alt="Photobucket"></a>

normally found below boiler or downstairs rad
[/img]
 