I have an extension 3.1 m wide and 5 long. Rafters will span back to front flat roof.

Will a 3 m catnic lintel be sufficient with 300mm returns on both sides and the rest for a French door.

The flat roof will be on the front wall above lintel but it’s a single story.
 
Sponsored Links
Joined
2 Feb 2006
Messages
45,200
Reaction score
3,100
Location
Staffordshire
Country
United Kingdom
Will a 3 m catnic lintel be sufficient with 300mm returns on both sides and the rest for a French door.

The flat roof will be on the front wall above lintel but it’s a single story.

No. 300mm returns won't get past building control without SE input.
 
Last edited:
Joined
23 Feb 2012
Messages
10,529
Reaction score
1,715
Location
Manchester
Country
United Kingdom
No. 300mm returns won't get past building control with SE input.

If it is 300 measured externally, I doubt any SE would be able to prove adequacy, unless there were suitable ties between the flank wall and roof.
 
Joined
1 Sep 2010
Messages
22
Reaction score
1
Country
United Kingdom
Returns will need to be at least 675mm each side, measured on the outside. The document reference is Approved Document Part A, diagram 14.
Download it for free here: https://www.planningportal.co.uk/info/200135/approved_documents/62/part_a_-_structure

For a 3m span generally it's best to go with a structural engineer to provide you with calculations to submit to building control, especially if you are installing bi-fold doors, as the beam/lintel can be designed to the manufacturer's deflection criteria to stop the door sticking.
 
Joined
3 Sep 2006
Messages
35,936
Reaction score
4,978
Location
West Mids
Country
United Kingdom
My philosophy is that they would not make 3m lintels if you couldn't use them. :rolleyes:
 
Joined
1 Sep 2010
Messages
22
Reaction score
1
Country
United Kingdom
Lintels are made to have a quantity of masonry over the top to spread the load. For a single storey flat roof that is generally not the case. Secondly, and this is why I mentioned it, lintel manufacturers won't tell you how much it will deflect, so you could end up with problems with binding on bi-fold or french doors. Thirdly, even if you go for a standard lintel, someone has to work out the loading.

Edit: Case in point today, I just rang Keystone to get the I-value (stiffness) of their standard cavity lintel, to see if it would go over a 4m bi-fold door. While it's advertised as going up to 4.8m long, the technical department said their charts didn't go up to a 4m lintel and they would have to "Get back to me". I have a few friends who used to work there, and one of them said that they tended to do a special for anything that long - which is no use to most builders as they want to get them off the shelf and not have to order it.
 