Hi
I'd just like to canvass some opinion as to the 'trades' resolution to a problem a friend's having with an electrician.
He had a flat re-wired and two boards installed - one for heating (E7) and another for the remaining circuits (24h). Both are protected by a 100KMF with 60A fuses inside.
After switching everything on, a day or two later the E7 fuse blew in the middle of the night. The electrician came back and put a clamp meter (he called it a 'load monitoring device' ) on the tails which read 78A. So he's agreed to do some remedial works.
His resolution is to put two of the storage heaters onto the 24h board and install a timer. Obviously this isn't an ideal solution on a new installation, but the electrician doesn't seem keen to replace the cable run from the KMF, which is 16mm T&E at present (he mentioned he couldn't terminate SWA successfully (agreed), but seemed to forget about the possibility of using meter tails!)
The run from the KMF to the E7 board is 8m through a bathroom (behind a removable panel) and a short lenth of ceiling void.
Do you think too much is being asked for here, or would you be happy with your installation if you left it the way the electrician is proposing?
I'd just like to canvass some opinion as to the 'trades' resolution to a problem a friend's having with an electrician.
He had a flat re-wired and two boards installed - one for heating (E7) and another for the remaining circuits (24h). Both are protected by a 100KMF with 60A fuses inside.
After switching everything on, a day or two later the E7 fuse blew in the middle of the night. The electrician came back and put a clamp meter (he called it a 'load monitoring device' ) on the tails which read 78A. So he's agreed to do some remedial works.
His resolution is to put two of the storage heaters onto the 24h board and install a timer. Obviously this isn't an ideal solution on a new installation, but the electrician doesn't seem keen to replace the cable run from the KMF, which is 16mm T&E at present (he mentioned he couldn't terminate SWA successfully (agreed), but seemed to forget about the possibility of using meter tails!)
The run from the KMF to the E7 board is 8m through a bathroom (behind a removable panel) and a short lenth of ceiling void.
Do you think too much is being asked for here, or would you be happy with your installation if you left it the way the electrician is proposing?