What's a comp vent?

Joined
15 Sep 2005
Messages
15
Reaction score
0
Country
United Kingdom
Recently had boiler serviced by BG (in my absence) and was left a note to say not to current standard - comp vent under size....hence my question.

TIA

Peter
 
Sponsored Links
Thanks for that and sorry for the delay in my response. Yes its in a cupboard - with louvred doors
 
If it's open flued, What kw gross heat input is it, devide by 1.1 multiply by 20, that is size (cmsq) of bottom vent to a room, half that for top vent. no fly screen, holes must admit a 5mm ball.

then room it's in must be vented top outside 5cmsq/kw after deducting 7 kw from the figure above.

There's a starting point.

we need more info from you tyo be specific. the less you give us the less we can help.
 
Sponsored Links
We have this when our boiler is serviced each year. Each engineer says vent not to current standards but when I ask if I should do anything about it say they wouldn't bother. Say still perfectly safe, I always find it confusing that they tell me but then advise doing nothing about it.
 