I get you now.Spark123 said:Sorry, see edit !
Yes. It would be the wrong thing to do.scotster said:So do I conclude changing the fuse to 45A is a non-starter?
Junction boxes are not favoured for such a high load application, because of the risk of a poor (high resistance) termination (connection) and the heat that would be generated; also the tendency for them to end up being inaccessible.scotster said:I assume sticking a large junction box in line of will derate the 6mm cable? The junction box would be acting as a straight through connector to a new lenght of 6mm to extend it by a few metres.
That would be the best solution, by far.If I cant do that I may as well run a new length of 10mm anyway as the 6mm wont reach the new switch position....
Softus said:Junction boxes are not favoured for such a high load application.
They make 60A ones.ColJack said:just out of curiosity then... do they even make 45A JB's?
For joining cable runs....and if so, why?
Softus said:Junction boxes are not favoured for such a high load application, because of the risk of a poor (high resistance) termination (connection) and the heat that would be generated;
In that case, please feel entirely free to recommend the use of a JB to scotster. I'm sure he'll be delighted to hear from you.equitum said:Personally I don't have a problem with the JB.
Since it's likely that you already know the answer, why don't you ask the question you really have in mind?(ps. after crimping should you wrap the whole lot in tape or heatshrink or other?)
Softus said:Eh? A non-faulty 9.5kW shower, even on full chat, will definitely trip a 32A breaker, even on 1mm² cable.John_D said:A 9k5 shower on stage 1 heating will probably not trip a 32A breaker on a 6mm cable
ps. after crimping should you wrap the whole lot in tape or heatshrink or other?)
Since it's likely that you already know the answer, why don't you ask the question you really have in mind?
The basis was my incompetence in construction of that sentence. I was attempting to point out that the cable size was irrelevant to the let-through energy, and made a hash out of it.davelx said:According to the curves on page 199 of the regs, a 32A type B will not trip for >10000 seconds at 41A, so I'm interested to know the basis of this statement.Softus said:Eh? A non-faulty 9.5kW shower, even on full chat, will definitely trip a 32A breaker, even on 1mm² cable.John_D said:A 9k5 shower on stage 1 heating will probably not trip a 32A breaker on a 6mm cable
I was misled by the word "should" - it seems that you meant to ask "do", or "would", in which case my personal answer is heat shrink sleeving (if I don't forget to put it on the cable ), otherwise self-amalgamating tape.equitum said:I don't know the answer, have done both, just curious to know what others do, thought that was the idea of a forum ?
davelx said:Softus said:Eh? A non-faulty 9.5kW shower, even on full chat, will definitely trip a 32A breaker, even on 1mm² cable.John_D said:A 9k5 shower on stage 1 heating will probably not trip a 32A breaker on a 6mm cable
According to the curves on page 199 of the regs, a 32A type B will not trip for >10000 seconds at 41A, so I'm interested to know the basis of this statement.