Hi all - hoping you can provide some guidance on a rather strange problem!
I have a open vented CH system, with a feed and expansion tank in the attic, the hot water cylinder and pump in the airing cupboard on the first floor, and a boiler on the ground floor. The pump is mounted vertically, and pumps downwards. There's a vent pipe from just above the pump. We've been in the house three years, and the only real playing around I've done was to move a radiator about a year ago, and I drained and refilled the system back then, but it was fine.
The heating is set on a timer to come on between 5:30am and 8:00am, and again at 5:00pm and 10:00pm.
About two months ago, the pump started waking me up in the mornings when it came on - it's whining very loudly, as though it's straining. On top of this, the downstairs radiators don't get hot - only the upstairs ones. Hot water is absolutely fine.
Once it's woken me up, it's been on about half an hour, and I get up and switch the heating off. The pump stops, and then I hear a gurgling/bubbling sound in the airing cupboard, as though air is travelling upwards from the pump. It lasts about 4 or 5 seconds, and is quite loud and distinct. Recently, the pump has started coming back on for a couple of seconds as well, even though I've turned the heating off.
Once this gurgling has stopped, if I then turn the central heating back on again, the pump is quiet, and all the radiators get hot - and everything works fine, and I can go back to bed.
This only happens when the heating comes on in the morning - not when it comes on in the evening, which makes me think it might be temperature related, as it's currently very cold at night?
I've bled all the radiators, and there's no air in any of them. I've looked down the vent pipe when I turn the heating off, but no water comes out. The pipework in the attic is lagged, so I don't think anything is freezing. I haven't done anything to the plumping recently to cause a change.
Has anyone got any thoughts what might be causing this?
I have a open vented CH system, with a feed and expansion tank in the attic, the hot water cylinder and pump in the airing cupboard on the first floor, and a boiler on the ground floor. The pump is mounted vertically, and pumps downwards. There's a vent pipe from just above the pump. We've been in the house three years, and the only real playing around I've done was to move a radiator about a year ago, and I drained and refilled the system back then, but it was fine.
The heating is set on a timer to come on between 5:30am and 8:00am, and again at 5:00pm and 10:00pm.
About two months ago, the pump started waking me up in the mornings when it came on - it's whining very loudly, as though it's straining. On top of this, the downstairs radiators don't get hot - only the upstairs ones. Hot water is absolutely fine.
Once it's woken me up, it's been on about half an hour, and I get up and switch the heating off. The pump stops, and then I hear a gurgling/bubbling sound in the airing cupboard, as though air is travelling upwards from the pump. It lasts about 4 or 5 seconds, and is quite loud and distinct. Recently, the pump has started coming back on for a couple of seconds as well, even though I've turned the heating off.
Once this gurgling has stopped, if I then turn the central heating back on again, the pump is quiet, and all the radiators get hot - and everything works fine, and I can go back to bed.
This only happens when the heating comes on in the morning - not when it comes on in the evening, which makes me think it might be temperature related, as it's currently very cold at night?
I've bled all the radiators, and there's no air in any of them. I've looked down the vent pipe when I turn the heating off, but no water comes out. The pipework in the attic is lagged, so I don't think anything is freezing. I haven't done anything to the plumping recently to cause a change.
Has anyone got any thoughts what might be causing this?