Wire up a pump to old boiler controller

Joined
10 Jun 2005
Messages
90
Reaction score
5
Country
United Kingdom
I need to wire up the CH pump back in to the boiler controller board.

In the schematic, it's plainly laid out as 7(N) 8(E) 9(L)

The bit that is making me doubt myself is the room stat wiring. In the photo there's an earth conductor on #7. Has whoever installed it before we moved in just forgotten to sheath the earth with a blue cover? I've looked at basic room stat wiring diagrams and it shows 1 live and two neutrals.

If anyone can guide me I would appreciate it as it's getting colder and mum wants the heating on soon.
 

Attachments

  • Screenshot_20251014-132346.Files by Google~2.jpg
    Screenshot_20251014-132346.Files by Google~2.jpg
    86.7 KB · Views: 17
  • IMG_20251014_130700217_AE.jpg
    IMG_20251014_130700217_AE.jpg
    299.4 KB · Views: 16
  • IMG_20251014_134821134_AE.jpg
    IMG_20251014_134821134_AE.jpg
    161.8 KB · Views: 19
Last edited:
Looks to me like they've used the 3-core flex to the room stat so brown - live, blue - switched live, g/y - neutral. Yes, they should have been oversleeved at minimum.

In the schematic, it's plainly laid out as 7(N) 8(N) 9(L)
7 - neutral
8 - earth
9 - live
 
Looks to me like they've used the 3-core flex to the room stat so brown - live, blue - switched live, g/y - neutral. Yes, they should have been oversleeved at minimum.


7 - neutral
8 - earth
9 - live
Thanks for both. The 7,8,9 labels was a stupid error to type. Thanks.
 