Hi, quick question, we are renovating our house, and whilst a full rewire is on the cards, we want to sort the kitchen out first.
My thoughts are partly because of the additional appliances, and the impending rewire. we add a second smaller consumer unit in the kitchen to run everything off so everything from there is new, and once the rewire goes on, then this area will already have been completed.

we will be running the following appliances from the new consumer unit.
1 x american fridge freezer
2 x single ovens
1 x microwave combi oven
1 x 5 zone electric hob
1 x dishwasher
3 x pop up socket systems ( comprising of 3 sockets on each)
1 x extractor fan
12 x spotlights
1 pendant light
2 x double sockets.
1 x bulkhead for outside..

Distance between old and new consumer units roughly 15m

what thickness twin and earth do we use in between the consumers... ( i understand cooker loads vary, so best guess would be great for now)
thanks
Mark
 
Sponsored Links
Joined
20 Sep 2014
Messages
2,086
Reaction score
213
Location
uk
Country
United Kingdom
You would be better running the circuits back to the main CU position and replacing it now.

DS
 
Joined
21 Feb 2007
Messages
50
Reaction score
0
Location
Herefordshire
Country
United Kingdom
Cheers for the quick replies.. if not using twin earth then what for a dist circuit?

Ideally i would go back to main CU but in theory i would have to replace each ring main for the hole floor (light/sockets/cooker) to do that... as the kitchen sockets are on the main ring main, lights on lighting one etc.... i just thought doing it this way meant i wouldnt have to touch other rings till we did the main rewire....
 
Joined
20 Aug 2009
Messages
9,280
Reaction score
1,191
Location
Dorset
Country
United Kingdom
Why can't you temporarily connect the old circuits to the new consumer unit?

That said, it does seem a fair distance from the kitchen to the mains position, so kind of understand why you want a kitchen consumer unit - typically called a sub main.
 
Joined
28 Jan 2011
Messages
50,201
Reaction score
3,363
Location
Buckinghamshire
Country
United Kingdom
Personally I wouldn't use any cross-sectional area of T&E for a distribution circuit.
Singles are probably easier to install, but if 16mm² were adequate, then I think the only other reason for rejecting T+E would be if the CPC was not adequate for the distribution circuit.

Kind Regards, John
 
Sponsored Links
Joined
27 Sep 2004
Messages
1,300
Reaction score
83
Country
United Kingdom
It would. However, unless there was some other reason for wanting to use SWA, it would seem a bit OTT to use it just to get an adequate CPC.

Kind Regards, John
The submain is likely to have to be on a 30mA RCD unless it is swa, which is obviously far from ideal.
 
Joined
28 Jan 2011
Messages
50,201
Reaction score
3,363
Location
Buckinghamshire
Country
United Kingdom
"likely" might be described as an assumption ... as likely :sneaky:
Sure, but it is the basis on which it's being assumed as 'likely' that I was asked about.

I have several distribution circuits in my (large) house which are run in 16mm² singles, but nothing about the routing of those cables, per se, requires them to be RCD protected. So am I perhaps the exception that proves the 'likely' rule? :)

Kind Regards, John
 