worcester 240

H

hav it

hello

m8t having problems with his 240. hot water is running ok but no central heating. If you push the advance button to select heating the little light comes on but no fan ect. room stat not clicking. I think it could be the central heating overheat stat faulty. ta john
 
Sponsored Links
Sponsored Links
Assuming you have the manual, go the electrical connections on the boiler where the "call for heat" signal arrives, and check it's there.
If so, check the microswitches on the diverter aren't sticking.
Check the CH thermistor (or is it thermostat?) isn't telling the boiler it's hot already.
Then give up, and read the instructions ;)
 
i think its the ch thermostat. But was asking for another opinion, The only thing thats was putting me of was the wall stat is not clicking
 
You need a voltmeter. Opinions are nowt.
Is is by any chance a Drayton stat with a big dial, about 75mm across? They don't clilck if the power's disconnected.
 
cool can you test thermistas the same way or not. cause i think the ch stat in the boiler could be faulty.
 
But room stat not clicking says it isn't getting volts - presumably comes from programmer - remove room stat and check.
If its getting hot enough for HW then it should for CH - usually the ch is the system stat.
Check the diverter valve is returning to CH position and its microswitches are working ok. COuld be that switch which sends mains out to stat - don't know.
 