• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

worcester 24cdi

Joined
10 Jan 2004
Messages
4
Reaction score
0
Country
United Kingdom
i have a worcester 24cdi 2 years old
the DHW rate has dropped to 5lts per min. is this a common fault with these boilers and is it easy and cheap to fix, or hard and exspensive.
 
What's the flow like from your kitchen cold tap?
Are you in a hard water area?

The classic cause of restricted flow is scale in the secondary heat exchanger, but two years is a bit soon. It isn't hard to take it out and have a look. The restriction could be somewhere else, but I haven't heard of anything in particular - worcs boffs may know different!

If you decide to replace the heat exchanger I can sellyou a new one for half the new price.
 
there is a filter in the diverter valve assembly which is normally the first thing to block up....needs to be drained first though. you could also try adjusting the flow adjuster on the dv with a screwdriver, it turns about 1/4 of a turn check the manual. If you open it full and don't get your 9 lpm it's a draindown
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top