worcester 24i rsf (2 probs)
  • Thread starter Thread starter B.O.B DOLE
  • Start date Start date
B
B.O.B DOLE
the first is once fired up it cuts out after 10 secs then the ignition starts to spark and does not light up also the fan stays on running
the second is if i fire it up this is on another boiler for dhw it is ok but if i turn the dial onto ch only there is no response from boiler at all
the pump is ok in each case
any ideas
No1...
Check for correct polarity, flame sense electrode and sensor lead. All ok? I would say PCB. (According to Ignition check page 31 of the manual).
No2
Something simple first. Check the CH dial hasn't actually snapped and is not turning the CH pot on the board...come across it a few times on these boilers.
jiminblack said:
No1...
No2
thanks for your response i have checked the flame sensor and is ok
do you think the solenoid could do this closing donw the gas supply
on the second could it be the selector switch not changing over
Have you got the manual? If you have the fault finding section is good. It's all the Worcester engineers use to be honest. If you haven't got one I'll email you one.
got one thanks
No 1 Fault....Check the voltage for live output on X5 pins 1 and 2 relative to neutral on Pin 3. If no voltage PCB. If there is good voltage and no gas pressure at input to burner then Gas valve.
it turned out to be reversed polarity to q1
Glad it's sorted mate. It's amazing how many times we come across reverse polarity!