Worcester Bosch Greenstar 24i System - condensate trap

Discussion in 'Plumbing and Central Heating' started by chuckstardeluxe, 15 Feb 2021.

  1. chuckstardeluxe

    chuckstardeluxe

    Joined:
    31 Oct 2016
    Messages:
    10
    Thanks Received:
    1
    Country:
    United Kingdom
    Evening all,

    Condensate trap on the boiler is full of crap (as per photo) and we are getting EA messages related to the condensate exiting - probably due to freezing but this could also be causing an issue.

    Manual is fairly unclear on whether boiler will refill the trap automatically as part of a program, or I need to manually fill the trap before turning back on.

    We are self isolating - hence can't get a plumber over.

    Thanks in advance
     

    Attached Files:

  2. Sponsored Links
  3. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    12,928
    Thanks Received:
    2,906
    Location:
    Daventry
    Country:
    United Kingdom
    It does have a trap filling program, which will kick in if you turn the boiler off for a few minutes then turn it back on again. Be careful emptying that, there's quite a bit of water there and if you get it wrong it can get into the PCB. EA is most likely a frozen condensate, there's not so much dirt in that trap that it would completely block the flow
     
  4. chuckstardeluxe

    chuckstardeluxe

    Joined:
    31 Oct 2016
    Messages:
    10
    Thanks Received:
    1
    Country:
    United Kingdom
    Thank you - I’ve disconnected the rubber gator which fits over the pipe and diverted that into a bucket for the condensate whilst we have this freezing weather which seems to have sorted things.

    I’ll leave the draining of the trap to a professional at the next opportunity!
     