Worcester Greenstar Junior 28I Combi Boiler and Honneywell r

Joined
1 Mar 2009
Messages
3
Reaction score
0
Location
Surrey
Country
United Kingdom
I had new boiler (Worcester Greenstar Junior 28I Combi Boiler Natural Gas) installed and I have connected it to the existing Honeywell T6360 room stat. The boiler has WB digital programmer fitted. Now it looks like the thermostat does not control the heating. i mean that the boiler is running constantly no matter what temperature is set on the stat. the boiler and the stat are connected by two wires cable at the moment. I have connected them according to the boiler's manual. Can anyone tell me what have I done wrong? Many thanks
 
Sponsored Links
When you connected the stat into LS and LR did you remove the link that was in place? If not this needs to be removed.
 
When you connected the stat into LS and LR did you remove the link that was in place? If not this needs to be removed.



Thanks so much Jamespl. Spot on. As soon as I removed the little bridge connection it was ok.
 