Can i use Denso tape to cap over wires which will be plastered over? I dont want to use galv capping is the wire runs in ackward lines.
Thanks in advance
Is Denso tape like insulating tape? If so then you cannot do this.Can i use Denso tape to cap over wires which will be plastered over? I dont want to use galv capping is the wire runs in ackward lines.
Thanks in advance

Does the foil in Flexishield provide greater mechanical protection than steel capping?
BAS knows that (522.6.6) - he's just being awkward!

Properly applied denso tape will maintain its water barrier for many many years. The buried steel water pipe to my property was laid in 1950, it was wrapped in denso tape, under the tape the pipe looks like it was installed last week.
I get the impression from the OP that the plan is to run cables diagonally, as I can't work out what else they would mean by "wire runs in awkward lines". If that's the case, galv capping (and certainly not denso tape!) will make absolutely no difference. You'd have to employ earthed steel conduit, mechanical protection, or use a cable with an earthed metallic sheath such as SWA or FlexiShield.
It's easy enough to show that the csa of capping makes it OK for a cpc - there are no tests of conformance required.
Likewise there are no specifications for mechanical protection.
So we all accept that the foil in BS 8436 cable is OK, but steel capping is not?
Where's the logic, the reasoning, the engineering basis for that?
So we all accept that the foil in BS 8436 cable is OK, but steel capping is not?
Where's the logic, the reasoning, the engineering basis for that?