Hi are you sure you have set Parameter 3 as already suggested by boilerman2?
Do you know how to do this? using the +,- and enter buttons.
Paul Barker meant to say link 3 to 4 on X2 (see earlier posts).I tried the links ( 3 to 4 ) on X9 , but this just fired on the boiler constantly.
That is worrying. Have you checked all terminals on X2 for 230V?The strange thing I picked up from reading Paul's post and also the user manual was I should be able to feed a clock off pins 4[L] and 5[N] on X2 , but I have never had 230V on pin 4.
CorrectX2 : pin 1 s/l
X2 : pin 3 linked to pin 4
X2 has no other connections
Correct. X3 is not mentioned at all in the manuals.No blocks for X3 , X5 or X7 connectors
Are you sure you have this right? The wiring diagram on page 27 of the manual has it the other way round, i.e:X4 : pin 1 connected to white
X4 : pin 2 connected to black
X4 : pin 3 connected to brown
X4 : pin 4 connected to blue
CorrectX6 : Permanent Live
X6 : Permanent Neutral
Remove the link between 3 and 4 (see earlier in this post). The rest is correct.X9: pin 3 linked to pin 4
X9: pin 5 linked to pin 6
X9 : pin 7 linked to pin 8
X9 has no other connections
Where are you connecting the output from wiring centre term 8 to on the boiler?it's firing up the boiler from the 230V demand feed { from Wiring centre term 8 orange from 3-way valve }
Is the permanent live to X6?but when I feed a permanent Live , place the 230V demand in term 1 on X2 and remove the links.
What do you mean by this?It starts up but won't call CH or DHW
No mention of that in any of the installation manuals! According to them all boilers are set to 1 (CH on and HW on).The Parameters are settings in software used for different situations The 24S is factory set for 2=CH on and DHW off all the Avanta range use the same pcb's so the parameters have to be set to suit ie Combi, System,Ngas,Propane etc.
Not in my system/combi Manual! The table on p38 gives what the different P.3 settings mean and P42, 2.9.10, says how to reset the boiler to default settings.P40, 2.9.10 is the nearest you will get to telling you about setting the pcb for different models.
I have only just noticed that there are separate table for the Combi [page 37] and System [page 38] boilers! On the combi P3 is set to 1 and on the system it is set to 2. That makes sense.Hi D_Hailsham
Please look at page 38 of installation/ service book supplied with boiler
Just shows that you should never assume anything and always check everything. It's called "starting from from first principles".then it dawned on me , I have been looking for a boiler issue when all the time this was a power source problem , I confirmed this by testing perm. X6 feed { yes , it was reversed } .
##### brown and blue were reversed on the electric spur socket ######