16mm concentric cable supplies my mums house. It also supplies the 3 houses around her. Thats one cable, 4 houses, 1 phase. In a suburban area. Stop whining.
The agreed supply is 18,000 KVA.
What the hell are you supplying? A hadron collider or something?
19 volts drop at 45A equates to a L > N impedance of around 0.42 Ω .
So a PME conversion would not be straightforward affair - it would require some investigation as it is a tad on the high side when the supply N is doubling up as the supply E (although it would probably drop when/if the N was earthed at various poles)
Voltage issues
Declared UK voltage is 230V +10% / -6%
DNO has to respond to complaint and will fit a voltage recorder for about a week, make sure house is occupied whilst it is there!
Ratings of cables when used by DNOs are different to IEE ratings, a 16mm cable is good for 100A
Incoming supply rating, how do you know it is 80A?
Positioning of meter
Most DNOs are not too bothered but would actively discourage one being situated upstairs, as suggested the porch would be the best location,
Overall with the conditions as stated I would initially be looking for a poor connection on the DNO overhead cables