P
Paul_C
MCB's where mistakenly added to this table in the 1960's
Let me ask this question again: To which specific table in the 13th or 14th edition are you referring?
That he's a hopelessly ignorant t**t?And I still don't understand what point you are trying to make.
Paul,
The resistance of all of the other copper cables in the circuit is decreasing whilst the copper cpc is increasing???
I believe that the Fourteenth Edition was released in 1966.
Much lower than what?
The fourteenth Edition was approximately when MCB's where invented
when the Regulations were first expanded to their current format
This was also the Edition where the word radial was first misused!
OK,
During a fault of negligable impedance to earth, the cpc will get hotter than the line circuit conductor.
This process of heating the cpc takes time, this time will affect the automatic disconnection time of the over-current protective device.
Decrease the resistance of the cpc (Table 41C) and the cpc temperature will not need to increase as much, therefore logic suggests that the automatic disconnection time will not be affected quite so much.
Conclusion:
The R2 values (for fuses) given in Table 41C where measured not calculated.
Paul_C said:You are being asked to believe that during a fault of negligable impedance to earth the temperature of a cpc increases, but during this time the resistance of the cpc is increasing as the current flow is also increasing.
Which contradicts ohms law!
No it doesn't. The current which flows during the fault is determined by the overall resistance of the circuit, not by the resistance of just the earth conductor. It's the reduction of that overall resistance of the circuit due to the fault which results in the increase in current.
John,
An increase in heat must be caused by an increase in power, therefore the resistance must be less.
Otherwise you are telling me that to make something hotter takes less energy, which obviously makes no sense.
I believe there is a point to this conversation.Conclusion:
Is there any point to any of this, at least answer that