Cooker / Hob new radial circuit
26 Nov 2008
Cleveland
I need to add a new radial circuit for a hob and cooker.
The hob is induction type running at 6kw and the oven is 2.3kw
with diversity I make out the demand to be about 22.5amps
So should I just use 6mm cable and a 32amp mcb or should I future proof with 10mm while everything's in bits?
Cable run is about 10 metres and in free air under floorboards.
I'm intending on using a click easy fit dual appliance plate + spur off with 6mm to an unswitched socket (or fcu) for future proofing with a dual accessory box. - this ok ?
This would allow isolation via a single cooker switch mounted above the worktop.
The appliances came without cables attached (hob needs 4mm 3 core h07, and the oven needs 1.5mm 3 core h07) - Am I ok just putting the oven straight into the dual appliance plate or should it be fused via a fcu (or fix a plug and unswitched socket)? (the manual doesn't mention anything about fusing except that the oven needs 13amp)
6mm² will suffice as long as it does not run through ANY thermal insulation.
That's ok then.
Yes.
Very wise.
Yes - if you also use 4mm² cable for the oven.
The regulations say the Manufacturer's Instructions must be followed (although the above is electrically satisfactory) so an FCU or plug with the 1.5mm² cable will be acceptable.