Combi boiler in bathroom
Thanks so are you saying must boilers can be installed in zone 2 these days? I.e less than 0.6meters from the bath or shower?
Yes, remember i am talking about boilers, not timers or stats, which you would still need to check, unless you are using a non mechanical timer.
Most boilers and controls can be fitted in a bathroom as long as inside a lockable cupboard or compartment.
But before choosing that location remember hot steamy atmospheres are not ideal for electronic equipment.
Tony
Thanks for the help, how come ideal state, even if put in a cupboard they need to be installed beyond zone 2 further than 0.6meters from the bath but most boilers don't.
Ideal are not suitable to put anywhere, not just in a bathroom :lol:
It is because they do not have a suitable IP rating, where as say Glow Worm, which i think were the first, make sure all boilers have the needed IP rating for that zone.
I assume the isolator for the boiler would have to be in a suitable enclosure if in zones 1 or 2 ?
Regards,
NA
Anything permitted in Zones 1 or 2 has to be in a 'suitable enclosure' in order to achieve the required IP rating. If you're talking about an FCU, a switched one would not be allowed in Zones 1 or 2 and an unswitched one (hardly an 'isolator') would obviously have to be IPX4. The obvious place for an isolator is 'outside of the zones'!