Boiler does not fire when the controller is demanding Hot water. Heating is working correctly, ie boiler fires on Stat demand.
Boiler is Potterton Suprima 40L, open vented system with 2x2 MV. The valve for hot water is a Honeywell valve. As the wiring centre is near to the valve I have tested the voltage on the wiring and found the following:
Valve Wire Colour --> connect to wire in wiring centre
Grey x2 (1 to CH and 1 to HW valve) --> Blue
Brown --> Yellow
Orange x 2 (1 to CH and 1 to HW valve) --> Red
Blue x3 (1 to CH, 1 to HW and 1 to pump) --> Blue
with the controller selected to on HW demand:
240 volts measured on Grey to Blue and Brown to Yellow
with the controller selected to on CH demand:
240 volts measured on grey to Blue, Brown to Yellow and orange to red
I can only assume the problem with the HW valve is it is not supplying 240 volts on orange and red. Can someone confirm that my diagnosis is correct and indicate the likely problem with the valve? Can it be fixed or will it need replacing?
Thanks is advance