- Joined
- 10 Oct 2011
- Messages
- 16,396
- Reaction score
- 4,043
- Country
Check flow/return temps in d.40/41 when calling for heat (room stat cranked up high).
Okay at 14kw:-
D40 = 56C
D41 = 51C
However, has now dropped:-
D40 = 52C
D41 = 48C
Just to let you know, the room stat is set at 35C and all TRVs are set to 5 Max.
What burner triangle?? There is none.Is the burner triangle constant on left hands side of display?
So the rads are now heating with burner staying on?
Burner status symbol will mirror image bar status symbol.Here is the temperature of the Central Heating when the boiler was running earlier:-
This is getting hard work , good luck with it..
Can you confirm what make of controls you haveand also let us know the figure you have at D.009 when the boiler is firing.