cable routing behind plasterboard
26 Oct 2009
Hampshire
Hi, In my garage internal wall running down from ceiling I have a lighting cable to a switch and a power cable down to a socket both clipped onto a bare breeze block wall.
I would like to plasterboard the wall which will cover these cables, what do i have to do to make sure I comply with regs,
power cable is a spur of the ring, rcd protected,
lighting cable on downstairs lighting circuit 6a mcb
Many thanks
By safe zones, this would typically mean that the cables are in line vertically or horizontally with the accessory.
There are other safe zones, but the above is the common arrangement.
You should also replace the back boxes with metal knockout boxes, so once the boarding has been done, only the socket/switch faceplates can be seen.
For a top job, remove the cable clips and fit pvc capping over the cables. The wider capping is best.
Thanks for your replies, i am concerned though that the lighting cable is not rcd protected and will not meet the regs?
To comply, either
- add an RCD to the circuit
- install earthed metal conduit and put the existing cable inside it
- replace the cable with one which has an earthed metallic layer / armour as part of it's construction.
Thanks for the replies if I use metal capping will I have to connect an earth wire ie 1.5mm single to an earth point ie earth in socket or switch
Is this a detached garage or attached to your property? Do you not have a Garage Consumer Unit installed?
Sorry Taylor, you're correct, there's no RCD on the lighting circuit.
The drills okay, I tried to get some new titanium drill bits this weekend, and got given HSS drills instead. But yes BAS, I got this one wrong.