Isolation point for appliance
Status
Not open for further replies.
17 Jul 2011
London
hi fellas
I'm a heating engineer, just installed a new cylinder and controls in a basement, boiler is upstairs in the kitchen
My spark put the fused spur in the basement which would be normal in this example
Another spark has put us there to test and upgrade electrics, he is saying I need spur next to appliance
Can I put a label on the boiler stating isolation in basement ? Is it a reg?
Many thanks
Can you fit a DP isolation switch to the boiler supply?
IE, the cable from the spur in the cellar which feeds the boiler.. and label it something like supplied via fused spur adjacent to XXX in cellar.
There is no actual electrical regulation requiring local isolation as such.
However, where it is provided for maintenance, there should be only one device for the system and, where remote as in your case, it shall be capable of being locked to prevent inadvertent re-energising.
In your case, wherever you have one it will not satisfy the conditions for working at the other location.
You could fit the extra switch as wanted and label "not for isolation purposes".
They can always use the CU to isolate and lock the whole circuit.
The spark has said he would be happy if I put a double pole switch interrupting the boiler supply, I don't like the idea of two isolation points, someone could get hurt.
The boiler circuit is also on its own circuit from the consumer unit
If they are in series, how does that increase the chances of someone getting hurt?
So you've already got two isolation points - the MCB and the FCU.
Why was the FCU even installed in the first place?
What's the rating of the MCB for that circuit?
There was a spare space on the board, there was also a ring required in the basement as some other parts of the heating system needed their own fused spurs or sockets, it was deemed a good idea to put all the heating on its own circuit
The problem I foresee as an engineer is if I went to a breakdown I would see the spur at the boiler, turn it off and expect all of the controls to be isolated as well, this wouldn't be the case.
The spark thought it was a good idea to isolate all of the appliances and it was easy to do and the space, maybe over kill but it's done now
Fused spur for heating controls
Unswitched socket for accumulator pump
Fused spur for D2 discharge pump
Because if they are, how are they to be installed in countries where there is no such thing as fused connection units?
Status