Why doesn't your electrician know what to do?
Well he turned out to be a bit of d1ck. He sorts of reminds me of someone, but can't quite put my finger on it.
Some DNO's fit iso switches, some don't.
Best bet is to ring them and tell them you are planning a board change.
Ask if they can come out and isolate the supply while you fit an iso switch then return (or wait while you do it) and re-energise the supply.
Make sure the tails leaving the iso switch will be long enough to reach the main switch of the new board in its new position.
It is 4 pole as since it is a TT circuit, this is all that is needed.
You keep saying this.Meter to Fuse
Fuse to Isolator
Isolator to the CU
Please have another look.
So anything before the meter is their responsibility and anything after the meter is the customers?
I have a TT setup.
If both of those are true, the existing installation is unsafe. A fault to earth will not trip any of those MCBs, and will leave exposed metalwork with dangerous voltages.There is deffo no earth going into the breaker:
The rating of the iso switch needs to match or exceed the rating of the main fuse. To save any unnecessary expense, fit a 100A one.
Why do you need 4P?
Therefore your installation is potentially dangerous and should be turned off until it's made safe.So I have a TT setup.
Currently there is no RCD protection at all.