10mm shower cable
19 Oct 2011
Merseyside
i have recently installed a 10mm shower cable.
I was told by a salesman in a bathroom centre I can only run a 9.5kw or 10.5kw shower from a 10mm cable.
Is this true?
I have only installed the cable. When I'm ready, I will be getting an electrician in to connect it all up and install the correct fuse/switch in my fuse board.
Thanks for any advice.
Yes.
Unless the cable runs through (surrounded by) or is covered by >100mm. of thermal insulation.
The electrician should want to see the installation method before connecting.
Yes. Unless the cable runs through (surrounded by) or is covered by >100mm. of thermal insulation. The electrician should want to see the installation method before connecting.
Do/did you ever see (or install) 16mm² cables in shower circuits?
The cable currently runs from my fuse board (not connected) along the top of my kitchen wall in some white trunking, up through the ceiling/bathroom floor into the loft to the area the new switch will be, then another wire from where the switch will be over the ceiling and down the wall to where the shower will be. The cables are 12 meters and 3 meters long.
None of them or under insulation yet and as there is plenty of slack, them don't need to be, I can slide the insulation under the wires.
Can I use a 8.5kw shower?
I have upgraded the cable from 6mm because I was told I can't use a shower more then 8kw on a 6mm cable.
In time the kitchen ceiling will be replaced and the cable will go in the ceiling.
Can I use a 8.5kw shower? .... I have upgraded the cable from 6mm because I was told I can't use a shower more then 8kw on a 6mm cable.
Assuming that the cable in the roof is not covered in a lot of thermal insulation, then, given that some of your cable is in trunking, 6mm² cable (without any thermal insulation etc.) ought to be good for a shower up to about 9.1kW (at 240V). If the 6mm² cable were buried in a wall (or, as you suggest, moved to above the ceiling), rather than in trunking, it could support a shower up to about 11.2kW (at 240V).
No -
but rather than have to derate a cable because it in a particular installation method, I would regard the ratings tables as an indication not to use that installation method.
Sometimes it may be unavoidable, I suppose.
Is this true?
To clarify, as there seems to be some confusion later on, when the salesman said you could only run a 9.5kW or 10.5 kW shower from a 10mm cable he also meant showers below that rating (eg 8.5kW) are also ok on a 10mm cable.
To clarify further, a 10mm cable is the CSA of the live and neutral conductor of the cable.
I'm not sure that clarifies what the salesman meant.
You could run a 15kW shower on a 10mm² cable (method C).
You can run upto 11kW showers on a 6mm² cable (method C).
10mm² is often used as a submain supply for a whole flat.
Indeed. However, as I said earlier, in the context of the OP's situation, I think we are talking Method B - hence the figures I posted.