Oven wiring
2.5mm^2 is not permitted to be used with a BS1363 plug.
Whilst I agree that there will never be a reason for using 2.5mm² flex with a BS1363 plug (and one might struggle to get it to fit), what are you suggesting "would not permit" it?
Well, not to add to the debate, but there might be a reason, if you're making a 100m long extension (I haven't calculated the exact length)
But agreed I always thought plugs weren't designed for 2.5mm.
Yes, I had overlooked extension leads. If one is contemplating a potential load of 13A, then I would think one would need 2.5mm² (if not 4mm² - and getting that into a BS1363 plug would be next-to-impossible) for lengths much shorter than 100m (depending on qhat VD one was prepared to accept). By my reckoning, the voltage drop of 100m at 13A would be 41.6V with 1.5mm² (~18% of 230V)and 24.7V (~11%) with 2.5mm².
Their instructions are ludicrous. They state that in the UK a 2.5mm^2 flex should be used with a plug and socket or FCU. 2.5mm^2 is not permitted to be used with a BS1363 plug.
There is no requirement to follow manufacturers instructions, especially when they are wrong.
We do have Table 52.3 so you never know, but ... why would anyone actually prohibit such a thing?
Well, although I doubt that such is the case, someone might try to 'prohibit' it if they felt that the mechanics were such that 2.5mm² cable could not be safely terminated in a BS1363 plug.
As for who the 'someone' might be, I suppose there's the manufacturer's 'instructions', but what gets connected to a BS1363 plug is presumably outside of the scope of BS7671. Does BS1363 itself perhaps have something to say about this? Stillp?
I've certainly seen 2.5mm² flex connected to a BS1363 plug a good few times, and I even think I have seen 4mm² successfully crammed into one!
Well, they might 'feel' it but it is not the case.
I can't say I've ever looked at the instructions on wiring a plug.
Just seen Risteard's post so will await Stillp's possible reply -
unless you, Risteard, can quote the actual wording.
Not the latest version, note, although I very much doubt that this bit has changed:
I guess the issue is that you cannot assume that a plug will take > 1.5mm², as there's no requirement for it to do so.
I don't know if that forbids makers from producing plugs which can, or forbids users from using 2.5mm² if they find it does fit OK.
I've got a plug with that size in it, and it took some care to get it in. I don't see how 4mm² would ever fit.
That's correct.
It doesn't prohibit anything.
Back in the days when MK were a reputable manufacturer, they used to offer a plug that would take 2.5mm² flex - I well remember them, as a lecturer at the college where I was a technician had me make a number of 2.5mm² extension leads with them.
That's correct.
Back in the days when MK were a reputable manufacturer, they used to offer a plug that would take 2.5mm² flex - I well remember them, as a lecturer at the college where I was a technician had me make a number of 2.5 extension leads with them.
What plugs were those? I find it difficult to get a good fit around the post terminals MK have always used with anything larger than 1.5mm², particularly the live terminal as it then tends to foul the fuse. If I have to fit 2.5mm² in a plug I tend to use Duraplug or Permaplug as they seem to take it pretty well (though not sold on the quality of Permaplug).