Incidentally, the Motor has 3 connections marked 240v - N- 240v and earth.
There is a 240v to 110v step down transformer in the machine
OK, I pressed the wrong button, 240v.You clearly don't, because as has already been explained it is 240v.
No, just as with a UK 240-0-240 'split phase' supply (which the Wiring Regulations call '2-phase', even though a good few here say that is 'wrong'), relative to the "0" the two 120s are 180° out of phase.So what you are stating is that the USA 240V supply is not, as I had previously been informed a two phase supply, but a 120v-0-120v, with both 120`s being in phase, and any 240v appliance or load is connected between.
As above it IS correct, in that the voltage of the two outputs, relative to the centre tap, are 180° out of phase.Incidentally, I always thought the two output`s of any centre tapped transformer were 180 deg out of phase, is that not correct either ?
... and again, if you connect the 'common' of your scope to the centre tap of a transformer secondary (which is what will happen implicitly if the centre tap and the common of your 'scope are both earthed) and examine the voltages at the two ends of the secondary, you will find that they are 180° out-of-phase.I will put my double beam scope across a 110v site Tx tomorrow at work and have a look at the phase shift, if any.
Kind REgards, John
But why then has it got 3 connections excluding the earth, they are, a red wire marked L2, white wire marked N and black wire marked L1.
That is of course true, but relative to either end they are in phase and if we look at a transformer with 8 voltage tappings we would not call it a 9 phase transformer, it is still single phase.As above it IS correct, in that the voltage of the two outputs, relative to the centre tap, are 180° out of phase.
I have seen USA imports, and also seen them rejected due to the difference in what they call 120 volt and what we call 110 volt, we require the centre tap to earth, so we had a load of lighting sets with 110 volt outlets, then we found the 110 volt was not centre tapped it was taken off a centre tap so the generator was 110 - 0 - 110 it seems the question had be raised before buying "is this a centre tapped supply", and answer had be yes, and it was centre tapped but not the centre tapped needed for UK. All 110 outputs had to be blanked off, tried to get 110 to 55 - 0 - 55 volt transformers however they would need to be specials and so very expensive, and two phases were 190 volt not 220 volt so again needed special transformer, cheapest option was two transformers one 110 to 230 and second 230 to 55 - 0 - 55 so simply blanked off outputs and used as lighting sets only.Machinery imported from the US to the UK often has a 240 -> 110 transformer fitted to supply most of the machine's circuits as this is cheaper than changing most of the electrical items to be 240 volt devices. Where the machine also has 240 volt items that would use a 2 phase supply in America the machines wiring is altered to connect these 240 volt items to the UK single phase and Neutral
In the UK ~ Neutral----MOTOR----Phase
In the USA ~ Phase 1----MOTOR----Phase 2
You're welcome.Thanks John, I was beginning to think every thing I learnt in the 70`s was wrong.
I suppose that begs the further terminological question as to what one means by a "single phase transformer" and a "3-phase transformer".... with 230 - 0 - 230 we call it split phase when it comes from a single phase transformer and twin phase from a three phase transformer ....
I think you may be missing the point. ....That is of course true, but relative to either end they are in phase and if we look at a transformer with 8 voltage tappings we would not call it a 9 phase transformer, it is still single phase.
I will ask an American aquaintance, he is a service engineer aquaintance who roams the Eastern Seaboard.
Is he a lineman for the county?