All that plus the armour isn't much good at mechanical protection either.
SWA would appear to be not fit for purpose.
Winston overlooks every single thing which allows something to be done if he doesn't like it.Winston overlooks the problem that a fault in the cabin could trip MCB and/or RCD in the house leaving people in the house in the dark.
Why do you want a CU in the log cabin? Sockets can be run direct (using the MCB in the house) and lights via a switched FCU.
No required. As I said sockets direct (using MCB in house). Light(s) via switched FCU, and yes heater can be plugged into one of the sockets.
OK - so you're going to start off assuming something already in contravention of the Wiring Regulations, and in England & Wales arguably illegal.It can be a problem. Assume some minor damage to the outer sheath of the cable allowing ground water to reach the steel wire.
But even if not using it as the cpc, not earthing the armour is not an option.When the steel wire is connected to the MET in a PME system the steel wire will be at Neutral potential which may be a few volts different to the ground water in contact with the steel wire. AC galvanic corrosion will occur.
When the steel wire is connected to the MET of a TT system with a copper ground rod there will be a voltage generated from the cell created from dis-similar metals in electrolyte. Ground water being the electrolyte. DC galvanic corrosion will occur. Also happens if there is a lead water pipe or other metallic item that is buried and connected to the MET.
Incorrect - of course a larger circuit could be run to an outbuilding.once you want over 13 amp in the out building either RBCO in house or CU in outbuilding, the option of a simple MCB in the house is only valid if supply under 13A so a RCD FCU in house or outbuilding can be used.
Are Moles capable of chewing steel?
So we return to a scheme member electrician working on your home, is more limited than your self
Take your point.Do gardeners read a copy of the Wiring Regulations and thus know it is illegal to hit a buried cable with a spade. And I doubt moles can read anything
No I have not confused posts. Winston replied to a post recommending a CU, saying to take the swa into a junction box and feed into an fcu. For a shed, that could be viable, but this is for a log cabin.Are you perhaps confusing winston and eric, since I cannot reconcile your comment here with anything that winston has posted in this thread? It was eric who, for reasons I fail to understand, was talking about limiting loads to 13A - as far as I can make out winston only mentioned an FCU (fed from the cirecuit supply the sockets) in relation to lighting, which seemed fair enough.
I think I must be missing something, since all I've seen is ..No I have not confused posts. Winston replied to a post recommending a CU, saying to take the swa into a junction box and feed into an fcu. For a shed, that could be viable, but this is for a log cabin.
... no reference to a JB and, as I said before, he was suggesting that the sockets could be fed directly from an MCB at the house end, with an FCU for the lights (not to 'limit the load to 13A') fed from that. Obviously not the only way that it could be done, and perhaps not teh way that most people would do it, but I see nothing inherently wrong with that approach, do you?No required. As I said sockets direct (using MCB in house). Light(s) via switched FCU, and yes heater can be plugged into one of the sockets.
Just to be clear, you must earth the swa armour regardless of whether you also use a spare core for the cpc,
Also as I said earlier, have you considered the need for data/phone wiring.
It is.Ive heard some people say earth at both ends, others say only only one end. Maybe that is dependant on earth type.
Then it would have to be isolated at the cabin end.I wonder about the situation with earthing the armour when the earth isnt being exported, like a TT earth.