A point EFLImpudence brought up. The total value of the mbc's on a downstream sub CU protects the cable supplying the sub CU.
Totally correct but in this case the downstream OCP is to consist of a number of fuseways or MCBs, as yet we know not how many but let's make a random guess at 4, potentially they could all end up as 32A OCDs. IMO the minor additional effort and cost of 16 or 25mm² is a must.I would personally say (for a 'typical CU') "Yes" for the meter tails, main swithch and bus bars (since, at least theoretically, they could 'legitimately' serve a total load of 100A) - but that for "any cables off the bus bars" it would depend upon what downstream over-current protection they had (which could be a lot lower than 100A).
I agree. However I was responding to the general question about "any cables off the bus bars" - which, in some situations, could be protected by something of very modest rating.And in this case the downstream OCP is to consist of a number of fuseways, as yet we know not how many but let's make a random guess at 4, potentially they could all end up as 32A OCDs. IMO the minor additional effort and cost of 16 or 25mm² is a must.
Quite so, I have frequently added circuits to busbars of 1000's of amps with cables as small as 2.5mm²I agree. However I was responding to the general question about "any cables off the bus bars" - which, in some situations, could be protected by something of very modest rating.
I understand this comment but no I don't think it to be a necessity as that is what circuit design is all about. In a CU the 'full load' cables are usually burried behing the plethora of circuit cables and frequenly behind covers so it's not always easy to check their size. We then have the added complication that a significant percentage of domestic work is done by non qualified DIYers and with the greatest respect to much of their abilities [frequently better quality work than some qualitied sparks] checking the 'unprotected' cables will rarely be considered. We can, and I have encountered, decent 10 or 16mm² shower circuits in CU's fed by smaller cables [7/0.044" cotton & rubber main tails very recently and a few years back a 3 way sub FB in the loft conversion fed with 4mm² 32A fuse with a 45A fuse feeding a shower]Of course, one can always argue that once one has "a cable off the busbar", even if today it is connected to just, say, one 16A MCB (or maybe even just an FCU), someone might subsequently come along and use that cable to feed a 10kW shower through a 50A MCB. However, if one were going to try to design in a manner that anticipated any degree of future stupidity, we would probably have to wire everything, including lighting circuits, in at least 6mm² cable
I'll go as far as 50:50. Far too much of my recent work has been in rented property where all sorts of botches are to be found, such as:DIYer are rarely a problem. It is do-it-all know-it-all builders cutting costs, not getting in a professional electrician, I find are the biggest offenders.
Agreed. However, I would remind you that my comments were specifically about "a cable off the busbar" and one can but presume that the purpose of such a cable would (as certainly is the case with the OP's situation) virtually always be to feed something external to the CU.I understand this comment but no I don't think it to be a necessity as that is what circuit design is all about. In a CU the 'full load' cables are usually burried behing the plethora of circuit cables and frequenly behind covers so it's not always easy to check their size.
Yep, I'm happy with the first para. The case of a slave CU is different though, where both ends of the link between busbars may be hard to see, in fact as it's the first wire to be put into the second CU is may be completely obscured by circuit wiring, MCBs & bar cover and in the original it may be totally invisible behind the bar cover. In fact the reference to 2016 earlier the live link was completely obscured by covers, the neutral link between the N bars at the top of the enclosures was easy to see.Agreed. However, I would remind you that my comments were specifically about "a cable off the busbar" and one can but presume that the purpose of such a cable would (as certainly is the case with the OP's situation) virtually always be to feed something external to the CU.
The 'important end' of that cable would therefore not be hidden by anything within the CU, and anyone subsequently contemplating connecting something 'inappropriate' to the downstream end of the cable (outside of the CU) would presumably be guilty of the sort of idiocy which I said a designer cannot sensibly 'design against' by his/her design'.
No space for a separate mainswitch. Mainswitch is CU incomer. Sub CU needed. Can the one mainswitch incomer on the existing CU also switch the sub CU? That is, one switch does the two CUs. If so, what is the usual way of doing it?
Fair enough. I would again say that it really depends upon the actual situation and the extent to which one feels obliged to design in a manner that tries to anticipate future stupidity (rather than 'common sense').Yep, I'm happy with the first para. The case of a slave CU is different though, where both ends of the link between busbars may be hard to see, in fact as it's the first wire to be put into the second CU is may be completely obscured by circuit wiring, MCBs & bar cover and in the original it may be totally invisible behind the bar cover.
This was on page 4......This thread starts with `here is my solution, could you advise how to do it`
I would ask why you need a second CU and what circuits will be fed from it?
https://www.diynot.com/diy/threads/sub-consumer-unit.545529/page-4
- One Wylex CU, metal with eight single pole RCBs & one mainswitch incomer. Three years old.
- No space either side or on top.
- Only space available is under CU which can just fit another identical sized CU.
- Needs a sub CU under using the mainswitch (incomer) of the top master CU to switch out both. (have only one mainswitch);
- New sub CU will also be RCBOs, but the new DP.
- The sub CU can accommodate ten RCBOs, as no incomer fitted.