Hi Folks,
Looking for a bit of help here. We moved into our current house in 2018 and have always had a bit of an issue with the heating. The boiler is a Viessmann 200-W WB2B system boiler, and the central heating is split into the zones, each controlled by a thermostat. The boiler is plumbed as a two pipe system.
Along with huge gas bills, at times it seemed the heating would randomly come on, but never to full temperature...
The other day I popped off the cover from the CH junction box and was a bit surprised to see the following...
The three black cables coming in from the bottom are from the motorised zone valves for the central heating. (the DHW valve doesn't pass through this box). As you can see, the orange and grey wires are left unconnected... Also , the black wires coming from the thermostats are left unconnected too.
It's maybe not the best diagram, but here is what we inherited...
Now, to me it seems the thermostats don't actually talk to the boiler - from the junction box there is power to the Viessmann H1 External Extension, but no other connections.
So when the thermostats are turned up and click, the valves open and when the thermostats are turned down and click, the valves close, but they don't seem to tell the boiler this.
So it turns out the odd times of luke warm heating are caused by the central heating valves remaining open when the heating is off, but the DHW is on and in turn pumping round the central heating system.
Now I've figured this out I can stop it by turning the thermostats right down to zero when the heating is off, but it's not really practical.
So my question is... Normally, do the switches on the valves normally tell the boiler to fire when they are open and in turn the boiler tell the valves to close when the central heating is off?
The DHW pump and central heating pump (maybe the DHW recirculating pump too - I'll need to check) are all wired through the Viessmann H1 External Extension which in turn is connected to the boiler using the KM Bus. But there seems to be no connection to/from the thermostats/valves.
Surely they should be connected some how?
In the Viessmann H1 External Extension, there is a connection numbered 143 which in the manual is described as external blocking/external demand. There is nothing attached to this. Is this maybe where the valves/thermostats should be connected?
Obviously all this depends on readers knowing a bit about Viessmann boilers and components, but any advice would be very greatly received.
Thanks.
Thanks.