Thanks, that makes sense... I'll see how the hot water performs tomorrow and I'll update this thread accordingly...
I'm not entirely sure in as much as the boiler itself only has a dial that goes from Low to High (see photo) and doesn't specify any particular temperature... This is the setting I've had it on since the boiler was installed (set by the plumber who installed it) and previously it's worked without issue...May have been asked, what temperature is the boiler running at, ie the target or setpoint temperature?
It's 900 x 450 (36" x 18") so 120 litres...What size is the HW cylinder?
www.diynot.com
Yes, they both seem to be as hot as each other I would say...Is the other pipe ( mid way up) that connects to the coil also as hot as the lower Pipe from coil ?
It could well be, I simply did a hand touch to feel how hot both pipes were...I would expect a minimum of 10C difference
I assume you mean this one? I also assume I would do that when the boiler is not running is that correct? If I try that would I expect to hear a release of air if there is any trapped or for any water to seep out?You could always, with care, just slacken the top coil compression nut 3/4 of a turn at the cylinder and pull back the pipe to release any air, if present.
You have run it for 45 minutes?Just providing an update to this thread...
Having tried everything suggested above, apart from slackening the top coil compression nut 3/4 of a turn at the cylinder and pulling it back the pipe to release any air, if present I still have the same issue.
I decided to check the hot water temperature coming out of the taps this morning using a kitchen thermometer at it's only 45 degrees.
So despite the pipe with the two connections to the hot water cylinder and the air vent at the top being red hot to the touch when the boiler is running (I've not checked the temperature of that pipe yet) and the temperature on the hot water cylinder being set to 65 degrees, the water coming out of the hot water taps is 20 degrees lower.
Based on that would this still potentially suggest an airlock in the hot water cylinder since the pipe leading from the top of the hot water cylinder is hot but not red hot when the hot water taps are on and if so would draining the entire system and refilling it potentially clear any airlock?
Or
Could there potentially be a fault with the coil in the hot water cylinder and if so, how would you check?
Or
Is there any likelihood that the issue could be with the boiler itself? The fact that the radiators are red hot to the touch when on suggests not but I'm still trying to figure out possible causes and remedies.
Many thanks to all who've taken the time to respond, it is very much appreciated.
I did and yes, that resulted in 'proper' hot water the following day, but since then I've had it back on 20 minutes to see what real difference it's made and it's slowly reverted back to lukewarm water.You have run it for 45 minutes?
I'll do that in the morning when the boiler kicks in again.Check the boiler flow (outlet) temperature.
I assume you mean the 3-position diverter valve? This was replaced quite recently as it was faulty but is there anything I should check that could indicate whether it's become faulty again?You will have a motorized (zone) valve which stays open once HW is selected on and the cylinder stat is calling for water, you will either have seperate valves for the CH and HW or just one, called a mid position valve, with three pipes, try and locate these/this.
It's a Honeywell L641A1039 Cylinder 230 V Stat and it's currently set to 65 degrees.I cant see the cylinder stat scale clearly, what is it?, and what setting is it on?
I only seem to hear a single click when the dial is turned to approx 38 degrees or possibly if there are two clicks is within a range of about 35 to 38 degrees I would say.I cant see the cylinder stat scale clearly, what is it?, and what setting is it on?, turn the dial slowly anticlockwise (until you hear a click, note the reading, turn it back up slowly until you hear another click and note this, return it to its original setting.