The simple answer is it does not need a full rewire, the faults can be corrected. But the BS 7671 has a clear date after which the design must comply, note the design date not installation date, so in the main, if OK when designed, it is still OK today.
I say in the main, are there are exceptions, we are seeing one now, where some RCD are not suitable for reverse current flow, also where some thing has been clarified, like what is meant where we say the installation should be split into circuits. But unless it can cause danger, then not coded with C1 or C2, so RCD's tripping due to back ground leakage is not going to get a code C1 or C2.
It is also made clear it refers to electrical danger, lack of smoke alarms may be a danger, but not electrical danger. However HSE rules are where a danger is observed we must report it in writing, so including it in notes would I feel satisfy that requirement.
However I have only seen one court case report, and that was because the inspector had failed to report some of the faults, so I can see where the watch my back has resulted in an OTT report, but if reports even in notes, then it has been reported.
If I put in a report where I have worked wrong size fuse fitted, or label missing, unless followed by corrected, I would get a kick up the backside. Pointing out sample sockets had not earth sleeve OK as to remove every socket and fit earth sleeve would be rather time consuming. And if missed on sample likely missed on others.