Hello,
Had an EICR done on a property I am looking to buy. It is a 1930s 3 bedroom detached house. The electrician recommended that full rewiring be carried out which may cost around GBP8500. The report shows quite a few (7) C2 items but no C1 (items shown below). I was informed that the wiring is about 40 years old.
Are these issues more or less common and whether needs immediate attention or I can sort out later on? Also does the rewiring cost sound sensible?
Any help appreciated. Thanks
Had an EICR done on a property I am looking to buy. It is a 1930s 3 bedroom detached house. The electrician recommended that full rewiring be carried out which may cost around GBP8500. The report shows quite a few (7) C2 items but no C1 (items shown below). I was informed that the wiring is about 40 years old.
- Shower circuit is tap off in a 2.5 cable that feeds spur switch which does the shaver point C2
- fuse board no RCD protection C2
- fuse board (DB1) requires replacement not fire rated. (under the stairs) C2
- No power is present at the immersion switch further investigation required FI
- Kitchen light is on the kitchen sockets FI
- Utility light and the light under the stairs is on kitchen sockets FI
- Gas meter is not earthed C2
- Main earth is a 6mm earth C3
- Light fitting in utility has a burning smell when turned on C2
- x9 spot lights in the kitchen are not fire rated C2
- Socket in back bedroom the screws are corroded C2
- Water is not earthed C2
Are these issues more or less common and whether needs immediate attention or I can sort out later on? Also does the rewiring cost sound sensible?
Any help appreciated. Thanks