    I have received an unsatisfactory EICR report (with 12 nos C2 and 1 F1 code) and not sure should I get it done again by somebody else to get second opinion.

    Any advice (i.e. cost and genuine faults needs rectification) on that will be greatly appreciable.

    Poor condition of wiring, greening of cables in C/U and multiple socket outlets. No earth bonding to gas and water present. No CPC to multiple lighting points. Neutral conductor for ring final circuit has no continuity of conductors.

    16 Compatibility of protective devices, bases and other components; correct type and rating (No signs of unacceptable thermal damage, arcing or overheating) (411.3.2; 411.4; 411.5; 411.6; section 432.433) - C2

    17 Meter tails - F1

    19 Confirmation of earthing conductor size (542.3; 543.1.1) - C2

    20 Condition and accessibility of main protective bonding conductor/connections (543.3.2; 544.1.2) - C2

    23 Presence and adequacy of circuit protective conductors (433.3.1; Section 543) - C2


    25 Concealed cables installed in prescribed zones (see Section D. Extent and limitations) (522.6.202) - C2

    26 for all socket-outlets of rating 32 A or less, unless an exception is permitted (411.3.3) - C2

    27 for cables concealed in walls at a depth of less than 50 mm (522.6.202; 522.6.203) - C2

    28 for cables concealed in walls/partitions containing metal parts regardless of depth (522.6.203) - C2

    29 Provision of fire barriers, sealing arrangements and protection against thermal effects (Section 527) - C2

    30 Connections soundly made and under no undue strain (526.6) - C2

    31 No basic insulation of a conductor visible outside enclosure (526.8) - C2

    33 Presence of supplementary bonding conductors, unless not required by BS 7671:2018 (701.415.2) - C2



    Read more: https://www.diynot.com/diy/threads/eicr-report-advice.581701/#ixzz7CytCUL91
     

    Attached Files:

  2. Sponsored Links
  3. ^woody^

    ^woody^

    Joined:
    3 Sep 2006
    Messages:
    34,648
    Thanks Received:
    4,691
    Location:
    West Mids
    Country:
    United Kingdom
    May have got a better response if the OP just asked the sparks who did the test!
     
  4. rssteve

    rssteve

    Joined:
    3 Nov 2007
    Messages:
    660
    Thanks Received:
    19
    Country:
    United Kingdom
    Without seeing photos of these faults no one else can make judgement.
     
  5. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,949
    Thanks Received:
    1,128
    Location:
    Dorset
    Country:
    United Kingdom
    There's not enough info here to actually tell what the problems are and how they can be rectified.
     
  6. Robin0577

    Robin0577

    Joined:
    16 Aug 2011
    Messages:
    587
    Thanks Received:
    111
    Location:
    London
    Country:
    United Kingdom
    Impossible to judge without seeing pictures at least, but....

    "greening of cables" and "No CPC to multiple lighting points" both hint at an installation dating from the 1960s. IF that is in fact the case, then you should be prepared for some significant upgrade work.
     
  7. Sushant

    Sushant

    Joined:
    22 Nov 2021
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    See attached images and report.

    And being quoted a price of £700 which looks to me a rip off.
     

    Attached Files:

    • Report.pdf
      File size:
      955.3 KB
      Views:
      27
    • 3.jpg
      3.jpg
      File size:
      215.6 KB
      Views:
      51
    • 2.jpg
      2.jpg
      File size:
      247.5 KB
      Views:
      49
    • 1.jpg
      1.jpg
      File size:
      258.1 KB
      Views:
      47
  8. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,949
    Thanks Received:
    1,128
    Location:
    Dorset
    Country:
    United Kingdom
    The list you gave at the top of the page doesn't actually stipulate what actually needs doing, and more importantly, what he intends to do/put right.

    Your picture shows an out of date consumer unit with a small earth wire which I assume he wants to change.

    I don't know if he is intending on doing anything about the unearthed lighting cables and the green slime.

    Not to mention the other assumed faults which are not clearly described in the list.

    Just noticed the report in the attached files. Can't get the report to show up.
     
    • Thanks Thanks x 1
  9. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    37,323
    Thanks Received:
    1,306
    Country:
    United Kingdom
    I can't open the report either.
    :(
     
  10. Sponsored Links
  11. Sushant

    Sushant

    Joined:
    22 Nov 2021
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    No other paperwork is provided.

    He has confirmed following to be rectified in order to cover most of the C2 codes:

    1. New consumer unit with RCBOs to provide additional protection to electrical circuits.

    2. Lighting circuit not having continuity on the earthing.

    3. Meter tails and main earthing undersized.

    4. No gas or water earth bonding.

    5. Also told me to change downlights in kitchen, master bedroom/bathroom as they requires fire-rated light fixtures to be fitted.

    6. Green slime - Suggested for full re-wire

    In summary, get items 1 to 4 sorted to get a satisfactory report.
     
  12. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    10,080
    Thanks Received:
    2,033
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    Minimal descriptions on that report, but the main problems there are no RCDs for anything and no bonding to gas/water. Both of which have been required for several decades.
    No CPCs to lighting points would also need to be fixed, as does the open N on the ring circuit.
    Insulation resistance on 2 of the 4 circuits is far too low, and the only fix for green slime in cables is to replace all of the affected cables.

    Unknown what the £700 is for, but the only realistic option there is a new consumer unit and to install the bonding, and fix the other faults, which for the cables would involve rewiring
    If all that was quoted for only £700, then it seems excessively cheap.
    £700 for a new consumer unit and main bonding only might be plausible, but that would still leave the other faults unresolved.

    In summary, it's an early 1970s installation that should have been replaced a long time ago.
     
    • Thanks Thanks x 1
  13. markyd1

    markyd1

    Joined:
    7 Jul 2019
    Messages:
    136
    Thanks Received:
    9
    Country:
    United Kingdom
    green goo........rewire
     
    • Like Like x 1
  14. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,949
    Thanks Received:
    1,128
    Location:
    Dorset
    Country:
    United Kingdom
    £700 for items 1-4 sounds reasonable.
     
  15. Robin0577

    Robin0577

    Joined:
    16 Aug 2011
    Messages:
    587
    Thanks Received:
    111
    Location:
    London
    Country:
    United Kingdom
    Well if this is a property being put on the renal market, most letting agents won't touch a property that has no RCD protection on at least the sockets, so that means a new consumer unit. Green goo and lack of earthing to the lighting circuits point to a late 60s - early 70s installation so it's probably dur for a full rewire really.

    I'd say you're getting off very lightly at £700, when you should ideally be considering a full rewire costing a few grand.
     
  16. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    9,483
    Thanks Received:
    1,283
    Country:
    United Kingdom
    Cannot see any mention of 'green slime', what it does say is 'Poor condition of wiring, greening of cables in C/U and multiple socket outlets. No earth bonding to gas and water present. No CPC to multiple lighting points. Neutral
    conductor for ring final circuit has no continuity of conductors'.

    Or 'greening of cables in consumer unit'. that could be that the copper has suffered verdigris, or that green sleeving has been used, instead of green/yellow - anyone's guess. Without an actual quote detailing what he plans to do, it would be impossible to say whether it is good or bad value.
     