Help! Tuya thermostat wiring for a combi gas boiler - changing from honeywell thermostat to Tuya Thermostat 723 - photos attached
21 Jul 2024
I know simply ther live wire being brown will go to L and Blue wire from the honeywell will go to the Tuya N (neutral) point. However i am confused where to connect the ground wiring for the tuya thermostat. Safety's most important i assume in electronics/electrical. Help please thank you!
It is class II so does not need an earth.
The green and yellow wire is not earth, it is line out, rather naughty, this has not been permitted for my lifetime, and I am 72, if it were me, I would also be very naughty and wrap it in brown tape or sleeve and put it in terminal 4 and link 1 and 3, but that is not how it should be done.
You would need to run a new 4 core cable to replace the 3 core, and the rules say
A circuit protective conductor shall be run to and terminated at each point in wiring and at each accessory except a lampholder having no exposed-conductive-parts and suspended from such a point.
which since there is no terminal to terminate the earth to, is a bit of a problem, I suppose if a metal back-box then that will have a terminal? The original installer should be taken to court and made an example of, however the courts would be overwhelmed with plumbers.
Now this Tuya thermostat has already caused confusion...
Be careful here Eric, that would cause a big bang!
Terminal 3 on the Tuya might be labeled COM, but it is also labelled (N) - it is a Neutral out to power actuators.
The terminals to use are the potential-free contacts 6 and 7.
Do you have a wiring diagram on the rear of the Honeywell cover - something like?...
Thank-you, I had not realised this, I had just used the picture shown. cymru am byth
I seem to remember seeing three versions, and as @RandomGrinch says, they had different aims, and the timescale is important, I expect my oil fired central heating to heat a room from eco (17ºC) to comfort (20ºC) within an hour, but with under floor heating (UFH) it may take 4 hours.
So there is no one thermostat suits all.
It would be helpful if we could see the internal wiring of the thermostat (I am struggling to find one for any Tuya stat!)
Doesn't COM (terminal 3) just connect to OPEN (terminal 4) or CLOSE (terminal 5) depending on if there is a call for heat? So though its labelled "(N)" is there an internal connection to N (terminal 2)? If not then could you not just connect L to COM (and jumper to L (terminal 1) as suggested by Eric) and then output L when heat is called for (this would suit me as my motorised valve and then boiler require 230V live not neutral from the thermostat).
Hijacking one thread is one thing but two gets all confusing with potentially multiple answers. Best starting a new one and link to these
This specific model is designed for straightforward connection to UFH systems; not to the motorised valves of a standard wet C/H system.
On thermostats with volt free switching, it is usual to have COM, NO and NC terminals. In this case the terminal is labelled (N) COM; it is confusing, but still electrically correct to have a common line, or common neutral connection.
The circuit diagrams in the instruction sheet wouldn't work if this had volt free switching - they can only work if the COM is connected to neutral.
Edit:
The confusion may have been noticed.
I've just found these clearer instructions from an updated manual...
And to completely Wrap it up, here is a photo of a Tuya PCB, that I posted on another thread, showing the common Neutrals connected on the PCB...