However, in this case the RCDs are in parallel, presumably with the live of one circuit connected to RCD 1 and the neutral to RCD 2. In that case both RCDs should trip. The only likely explanations if only one trips are
1) One RCD is faulty
2) The neutral is connected to a non-RCD bus bar
Watch the video
But both rcds trip in the videoThe video proves nothing. The OP is there at the CU, resetting a single ,tripped RCD. Try unpluging the vac, reset both RCD's, then plug the vac in.
I see what you mean but I am not sure that one wire in the wrong place with all the other wires correct means the RCDs are in series.No, they are in series, in the sense that current flows from the supply, through the live side of one RCD, through the load, through the neutral side of the other RCD, and back to the supply.
This is definitely in parallel:
Y - e - s - - - - but the RCDs are not in series. Is there a more accurate term for that.True, but the load is in series with both RCD's, until one of the RCD's trips.
That sounds logical but are there any numbers for the situation.It remains a race, even in 'parallel'. The first to respond, removes the reason to trip, the fractionally slower unit remains engaged/untripped. No two electro-mechanical items, will ever behave exactly the same, respond in precisely the same way.
If both RCDs have experienced the same fault but one has not tripped does that not mean it is unsatisfactory.
No, what are they?I'm sure you are already aware of the answer to that question.
But both RCDs tripped in this example despite one tripping 11.2ms after the other had presumably cleared the fault.Of course not, it simply implies that one, is marginally quicker to react than the other - the test figures confirm that, if they are accurate, and repeatable.
Its tripping or to be more precise its in to process of tripping once that process starts ie is over the 30mA required then its not stopping, the variation is down to the manufacturing tolerance of the RCD trigger, ie the solenoid and components, after all its near instant disconnection not instant.That sounds logical but are there any numbers for the situation.
Are there time factors for the duration of a fault which should cause an RCD to trip - or does it just need to recognise a residual current for a very short time and then continue with its tripping process?
According to the OP's test certificate one of the RCDs trips in 22.3ms and the other in 33.5ms so what happens in the 11.2ms after the fault has been cleared that still causes the second RCD to trip?