As I have a large gas double oven, which unfortunately cannot be replaced. I am forced to have electric. However as it has to occupy a 900mm hole a double oven would be ideal. But I do not have or could provide a 30A (or whatever) source for it (solid floor and no available capacity on CU)
Long story short, I will install 2 single ovens with 13A plugs attached already. I have a complete kitchen ring circuit and would ideally intercept with a double socket outlet to supply those ovens.
Would it be bad practice to have a possible 6 Watt drawn from said double socket outlet or should 2 singles be used in preference or what would a professional advise instead?
Not adviseable for several reasons. You say
possible 6 Watt, how did you calculate that? When I went to school 2 x 13 = 26, although the maximum current of both running together will never be at full whack.
I assume that the kitchen ring circuit has an MCB of 32 amps? Ring circuits are designed to provide current for DISTRIBUTED loads round the circuit. You would be concentrating a huge load (when both ovens are running) at a single point.
You don't say what else is on the existing ring. Large loads like washing machine, tumble dryer, even a kettle used at the same time as the ovens could easily trip the protection for the circuit.
So...
You need a separate circuit for those additional large loads. it may look like (to you) that an additional circuit is not possible, but there are many ways to add another circuit, a small additional CU is an obvious solution. Often, a re-arrangement of the existing CU can free up a slot.
A site visit would provide you with some options. An experienced electrician can usually be creative when it comes to cable routes.
Lastly, re double socket for two large loads. the answer is NO. The test spec for BS1363 sockets is requires a double-socket to handle 20A total load; the test conditions are 14A on one and 6A on the other. I would not even use a plug and socket for loads like this. An FCU is the way to do it (assuming a new circuit can be provided.
Sorry to be negative, but you wanted professional advice.