It won't trip an RCD, but could prevent an RCD from tripping when a fault occurs.Why should that trip a type ac RCD or any RCD?
It wouldn't - but see flameport's reply (but also my reply to him which I am about to write).Why should that trip a type ac RCD or any RCD?
As you will be aware, I've been trying hard to gain some understanding of the various 'Types' of RCDs, but am coming to wonder whether Type A ones are actually 'good enough' to achieve very much in many situations - so perhaps you can help me to understand? ...It won't trip an RCD, but could prevent an RCD from tripping when a fault occurs.
If that is true then the implication is that the RCD might well not trip if the underlying DC component of current is greater than 6mA. In the context of what we're discussing (a motor fed through a diode) I would imagine that the DC component is likely to be a lot more than 6mA, so does that mean that a Type A RCD would offer little/no benefit (over a Type AC) in such a situation?BS7671 says:
.... For RCD Type A, tripping is achieved for residual pulsating direct currents superimposed on a smooth direct current up to 6 mA.
As I've just written, on the basis of what little I know of the characteristics of a Type A RCD, it might even seriously affect the ability of a Type A RCD to trip!It will not cause it to trip, rather it will slightly affect its ability to trip.
I've been asking questions about the behaviours of these different Types of RCD ever since I first heard of them and, despite having done a fair bit of reading, I'm still not very much the wiser.Oh wow, it's strange to see someone else asking the same question I asked 100 years ago
Not only that, but the energy used by electronic devices is likely to be a small fraction of the total.For modern electronics which use DC, there is a small loss converting AC to DC. However this is tiny, and even if properties were connected to DC supplies the conversion would still be required, as whatever voltage was supplied to a building would not be what was required by the electronic device.
They are better than Type AC, but only of use in situations that do not have smooth DC.whether Type A ones are actually 'good enough' to achieve very much in many situations
It won't, and neither will anything else as they were never designed for or tested with anything other than 50Hz sinusoidal AC.BS7671 tells us nothing at all about the performance of Type AC RCDs in the presence of DC components (of any magnitude
Type A will work with pulsed DC which is what you get from a diode, there is no 6mA limit there.Type A ones are only guaranteed/'required' to respond to a residual current in the presence of a DC component of up to 6mA - which is presumably relative peanuts in the sort of context we've been discussing here.