Looped supply - power went off when DNO changed the meter next door.
25 Jan 2010
Bristol
DNO changed out the meter at my neighbours house, pulled main cut out and bing off went our power for 10 seconds. I was under the impression that the DNO fuse came after the loop join ie on the load side to the meter but seems not. Our meter went dark and stayed off for the hour or so he took to install the new meter.
Our inverter and house carried on chugging after a brief burst of relay activity, however the smart meter went off. So all I can assume is that the live was cut by the fuse pull and the inverter carried on seeing the neutral as connected and just acted like there was no grid import. We tested that at the time by isolating the grid supply and the inverter went off, with the grid connected but no live the inverter was happy enough to power the house.
So in this instance the bit of cable between our houses was still live with power from the inverter back feeding it.
So the question really is that safe, I would assume that the dno treats all incoming cables from the grid as live, however on a looped supply would the expect the loop to go dead after the feed cutout was removed ?
DNO meter chap seemed pretty oh well so what apart from not knowing there was a looped supply seems the map was not right.
May be ask your neighbour if you can look at their service head, seems odd that pulling their fuse would affect your home
Seen the service head looped supply, live was off during the fuse pull. As the neutral is bonded at the service head and the cpc is connected to to the supply sheath there is a earth stake along the looped supply cable or by the very fact that the lead sheath is in the earth.As the inverter requires a neutral earth bond to work in grid / off grid its seen that from the functioning neutral with its earth bond and just carried on.
Spoke to dno - seems that as the loop runs under both houses there will be a fuse in the early 50's head that protects the cable both from the start and another one at my service head, ie a 60amp fuse in my neighbours house. So when my neighbours house has its fuse pulled my electricity will go off, Asked if they were concerned about backflow in this arrangement and they said no, if they wanted to disconnect for maintenance then they would disconnect both L/N at the transformer as this would cause grid tied inverters to shut down Also all supply cable maintenance is treated as live maintenance at all times and as they also pointed out even with my neighbours cut out pulled the incoming side will be live in the head.
So basically perfectly safe.
Thank you for your reply, it was not what I expected, I would hope @flameport would find this thread and comment.
I know my own inverter has a load of little switches that set it to each country's requirements, and even G98 and G99 in this country are different.
I was under the impression that it needed to see voltage between minium and maximum 216.2 and 253, but it does seem there were some changes, so they don't just switch off, but gradually reduce output as the limits are reached, the problem which has been identified is called islanding, where a number of solar arrays see each other as the grid supply, so don't switch off. I was unaware a single inverter could (except for the EPS output) do this.
Well that was an phone call... seems that the advice given was not so much wrong as right and wrong. DNO called yesterday evening. Seems there is an isolation fault that they will fix and will unloop our supply. It seems that from my neighbours supply head there is a fair chance that my inverter was seeing the grid frequency but no amps due to the fuse being out. When these were installed this type has a very close proximity of connections so as they put it with degradation of the head due to age leads to isolation of the loop getting weaker. So whilst no/ little current was passed the degraded connections this still allows for induction/ direct between the incoming supply and the loop. Hence my inverter could see the grid frequency which it relies on and carried on trucking. The did'nt suggest it was something terrible as they will do it as a part of a general unlooping in the next 12 -18 months, they have been having problems with ev charger installs and g99 installs, authorising them then discovering that houses they did'nt expect or knew to be looped were.
In fairness when my house was built in 1949 inverters for homes where unheard off, record keeping was hmmmm. to be fair you would expect terraced/ semi's to be looped but not detached, seems the builders just got it in the post war boom, house a has power but house b does not - I know....
Still say its safe,
My son had something similar, old council house, been sold off for years, and he wanted to swap which room was a kitchen, and rewire the house, and it would suit to get wires off outside of house, so got and excepted a quote to move supply, which would end up making the DNO cable shorter and allowing it to use an outside meter box, so money paid, and rewire cables taken to new consumer unit location, and a temporary cable run from old location to new, until all completed.
He was not actually in a hurry, lack of funds, so it took around a year to 18 months for them to get around to the move. But on arrival found it was a looped supply, and next door had died, a new owner has laid a new drive, where the cables should have run, and an extension was half built where the looped cables ran, so to move his supply easy, but it left next door without a supply, and it seems no way leave in place for the cables between the properties they did not run that way on the plans, so job further delayed, then Colvid so he moved into my house, then he bought my house and had a tenant all which slowed things up more and more. I assume all done now, but don't know.
However it does seem DNO records are often wrong.
Yes it is not as uncommon as you might hope, with all of the services.
Where I live a lot of the housing stockis sandstone terrace house built about 1910 mostly but a good measure over the years of other uildings of newer ages.
The local council at the time used to supply the electrics before it became the Boards, records were usually quite decents but there again some assumptions were made.
I particularly remember a stop tap leak in the road and have to be dug up deep down for repairs, working on their charrts they isolated three stop cocks to isolate the one they wanted to work on, no joy . So consulting charts and considering how those assumption errors of yesteryear was a time consuming job and re-evaluating assumptions with more assumptions then tried again and they eventually got it "right" , that took a few days just to do that unseen extra works, and but diagrams in to help the updating of the original charts (hopefuly).
I`m sure similar things could happen with gas and electrics.
A bit like us sometimes when we breakdown a circuit to try to establish where the problem(s) might lay.
Once something gets added or ammended several times over the years it can sometimes bear no relationship with any apparent logical progression unless you happen to discover the timelines and goals at each step which could be a few years apart.
Doesn’t make much sense to me about the close proximity that they speak about, possibly a biscuit tin type cutout which has an odd terminal setup for the meter as originally the meter sat directly on top. Not seen these looped though personally but I work in SSEN south DNO area.
Well must admit I’ve not seen many looped ones either, well the look looped but unless you seen the next property they could be ringed instead. If you visit a looped property, it’s usually one looks normal and the other looks looped so you would likely only realise the loop possibility if you actually see both.
Exactly I did not know I was looped, nor did the dno as they upped my main fuse to 80amps for an new ev charger for a new car with a higher charging rate. DNO said it should be fine untill the get it unlooped as I have had an ev for 10 years but now precludes my neighbour getting an ev untill its done, 1st in and all that. 60amps between two houses the benefits of diversity.
Whether or not having a 'looped' supply has any significance presumable depends upon the cables? If all the cables are of adequate CSA, then there would presumably be no problem in having two (or more) properties 'daisy-chained', rather than fed separately from some cable 'in the street', would there?
I have an interesting situation here, but easier to 'see what is going on' because it's an overhead supply. The present situation has presumably arise as a result of 'history'. My house was once detached and even more massive than it still is now. However, in 1950 bits on both sides (kitchens/nurseries/servants quarters on one side, a 'billiards room' on the other side) were both sold off, with both (even the billiards room!) becoming 4-5 bedroom dwellings, leaving my house as what officialdom (like mortgage providers) somewhat laughingly call 'mid-terraced'!
Anyway, following those changes, the current situation is that there is a 4-core overhead ABC cable (components not looking more than about 16mm²) from a pole to the wall of one of the 'neighbouring houses', with connections from one phase and neutral going into that property. All three phases and neutral then travel a total of about 25m along the outside wall of the adjacent property in singles (again, look about 16mm², possibly 25mm²) to enter my house and go to my 'cutout' (actually just three separate fuse holders plus a neutral Henley block). Finally, singles (same size) from the supply side of one of my fuses, plus neutral from the block, exit my house again and travel about 10m along outside walls before entering and supplying the other adjacent property. My installation has 3 x 60A DNO fuses, and I suspect that the other two properties each have 60A 'cutout' fuses.
Hence, mine is the middle of three properties with their supplies 'looped' from one to the next. As above, if the cables are all 'adequate', I don't see anything wrong with that - although, as I've sort-of implied, I'm not convinced that the cables necessarily are 'adequate' - and that would/will presumably becoming increasingly doubtful if some of the three properties (none at present) wanted to have EV charge points?
The issue would be essentially the same, but easier to talk about, if only one phase were involved. As things are, I'm not sure as to what phases are supplying what, since I cannot really trace the singles. The 'worst possible' case is that both of the adjacent properties are using the same phase, that also being the phase of mine which is used much more than the other two. Conversely, the 'best possible' case would be for the adjacent properties being on different phases, those two phases being the ones least used by me. I suppose it is the 'worst possible case' that we need to talk about, since that is how things would be if only one phase were involved.
What do you think?
Yup it all sounds plausible radials, ring mains or whatever may be ok or not to add to . Only the DNO can tell. Us mere mortals can only see what we can see and estimate and assume what is what. On large estates etc the DNO might work to a figure of 2kw per dwelling or 3Kw each or something in between if they wish. With small numbers like 2 or 3 or 10 or 20 they will probably require larger power ratings in their assumptions, only they can decide. Not totally unsimilar to us deciding if one dwelling with 5 ring finals compare to the same dwelling with 1 ring final might or might not have similar maximum demands if all other considerations are approximately equal.
It may be helpful to have a look at the report into looped supplies : https://assets.publishing.service.g...twork-connections-research-summary-report.pdf
Its pointed out that looping can and often is not restricted to my interpretation but of a wider looping issue which seems to fit your model, not only are two houses looped but collections of houses are looped, effectively sharing a 60 amp circuit at various points. DNO are unaware of lots of their network, I found that out by chance. The cable between houses is may not be the issue rather the capacity of the local grid from the transformer. Which to properly unloop may need a new cable and house connections from the transformer. From my take it would appear that as with all things its either going to be rationing - which has happened not to me but my neighbour as I have the ev connection they don't and cannot.
I would also point out that I have a g98 inverter which pumps out 12amps to the grid from 11 ish when the battery is charged to 5pm. There is 1 other house in our row of 6 houses with solar, they have an export limitation of 16amps on their g100 install, ....are they happy about it, well seeing as the cost of a g100 is roughly double a g98 and to make that cost pay you are reliant on good export numbers no they are not. In this case what happens if all the houses start pumping out 12amps..diveristy goes out the window as the sun shines on all the house equally - what will give ?
So basically we will need as you point out, a 3 phase re cable from our transformer to each property.. in 6 houses that's not huge in the scale of things but its a fundamental policy driven ireallssue, has the dash for large home solar as a mitigation to energy prices been thought through ? Has solar / ev been miss sold as an investment for a lower consumer cost when the real cost lay's buried in the ground or floating in the air as in your case?
.... Its pointed out that looping can and often is not restricted to my interpretation but of a wider looping issue which seems to fit your model, not only are two houses looped but collections of houses are looped, effectively sharing a 60 amp circuit at various points. ....
Quite - although it could presumably be anything up to 100 A. More generally, I cannot think of any conceptual problem with having multiple houses 'daisy-chained' on one single-phase 'radial' circuit. However, although that would result in somewhat shorter cable runs, I imagine that that could well be more than 'cancelled' by the fact that the earlier parts of the 'chain' would presumably require meatier (higher CSA) cable - so, in terms of cost & copper, the 'usual' system might well be the best for them.
So basically we will need as you point out, a 3 phase re cable from our transformer to each property.. in 6 houses that's not huge in the scale of things ...
There is probably no need for a 3-phase supply to each property - 100A should be enough for almost every normal house. However, as above, the currently 'usual'system is probably the most efficient - i.e. with a 3-phase cable going 'down the road' and with each house have a short feed from one of the phase of it.
... but its a fundamental policy driven ireallssue, has the dash for large home solar as a mitigation to energy prices been thought through ?
I don't think any of this has been thought through properly.
For what my opinion is worth, you could well be right!