Popping noise and flickering lights but no fault found?
4 Jun 2026
Could someone advise me please? We had a EV charger fitted in over a month ago and ever since it was fitted the lights in the extension as well as a floor lamp plugged in the extension started flickering. Those are on 2 different rings. Also, the light in the dining room flicker too (another ring), not sure if it's at the same time. Not determined if any other lights are affected yet as the flickering is intermittent and difficult to replicate. I can hear a pop when they flicker. Not sure where the popping noise is coming from but I can hear it more if it's hot and the windows are open. The electricity metre is in the downstairs toilet (extension). The fuse board is in the hallway, on the other side of the wall the electricity metre is on. We had the electrician who did the EV charger come back and check things over but he couldn't find anything obvious and didn't know what it could be. It seems to affect 3 rings at least (got 11 in total), 2 of which are right next to each other and one on the other side of the board. The electrician says he didn't touch those sides of the board but when I watched him, he seems to have been ripping wires out right left and centre ! Where shall we start? What could it be? I would ideally like to avoid the house burning down while we're asleep.
PS. Not sure if relevant, we've got solar panels and the inverter is in the loft in the original part of the house, installed in 2011.
Many thanks
To me it sounds like a wire may be loose.
However I agree, get a 2nd opinion from an older electrician who may be more used to fault finding and will not have an issue with identifying an error from the previous electrician.
The popping noise and the lights flashing don't seem to be dependent on the charger being used. It seems the longer the lights in the extension are on, the more frequent the issue
The EV Charger was added to a replacement second CU right next to the main CU. The original Main CU has the "main" house on the left and the extension on the right. The second CU was about 15 years old and had just our solar PV on it but we were told that to add the EV Charger, we would need to replace it with a metal CU
Thanks for that.
I’d be very interested to know how the supply cables connect from the new CU to the incoming mains.
Could you take a photo from further away?
Get someone else.
Loose connections are not found by ripping wires out.
They are more usually found by poking things with a stick.
Loose wires do not fix themselves, the problem will get worse until something fails open, melts, goes on fire, or there is a big bang as the main fuse is taken out. Perhaps al;l of those things.
Thanks for that.
The solar comes in from above the fuseboard and you can't see the cables unfortunately. The tails come in from the cavity behind the main consumer unit.
Get someone else.
When he came back, he tightened some screws and and the flickering decreased. I think i noticed it only 2x in about 8 hrs of light being on. The next day my husband spoke to a different electrician and he recommended we rock the switches as they wear out sometimes or get stuck. Yesterday I only saw the lights flicker 1 with a little pop so it seems it's a combination of things. We've rocked the switched more today and see it the problem is still there. Sounds like it might be the switches worn out and need replacing. Thanks
Exceptionally unlikely.
If these 'switches' are those in the consumer unit, then the busbar is loose, or some buffoon has fixed the circuit breakers in and missed the bar connection.
This is a serious problem and requires immediate repair.
I came to a shower circuit that was tripping the RCD.
Felt the CU case, it was warm.
Turned out the MCB wasn't screwed onto the busbar properly, it was getting hot and tripping the RCD.
Long story short it turned out to be a supply issue. The popping noise was actually coming from down the road. We are not the only ones affected. Looks like when the council resurfaced the paths, they nicked a cable.