You can presumably read the markings as well as I can, so the answer must be 'yes'. The nature of the figures marked is such that they are obviously mm², not AWG.So I bought this crimp tool so I can connect Bonding back up correctly. Am I correct in thinking that the largest one is for 8-10mm?
It didnt come with one. The pictures and tool is why i am asking - the marking above the largest crimp reads 4-6Read the MIL (Manufacturers Instruction Leaflet) AND look at the pictures, there is your answer.
Thanks John. Was just making sure as the figures above that gap state 4-6.You can presumably read the markings as well as I can, so the answer must be 'yes'. The nature of the figures marked is such that they are obviously mm², not AWG.
Those 'jaws' look very odd. There are four marked sizes (0.5-1, 1.5-2.5, 4-6 & 8-10) but only the first three have obvious 'gaps', leaving one (at least, me - and probably you!) wondering what one is meant to use for the 'top' size range (8-10 mm²)Thanks John. Was just makibg sure as the figures above that gap state 4-6.
I wonder if the plural reference to "crimping die sets" may possibly mean that some changing of interchangeable die sets may be required?Precise crimping die sets and integral lock with self releasing mechanism ensure high-quality crimping effect after crimping repeatedly
Yes, i thought that too. Not very clear imo.Those 'jaws' look very odd. There are four marked sizes (0.5-1, 1.5-2.5, 4-6 & 8-10) but only the first three have obvious 'gaps', leaving one (at least, me - and probably you!) wondering what one is meant to use for the 'top' size range (8-10 mm²)
Who knows. Thats why i asked on here. Tbh, I wss with 2 minds as to send them back, but since they will do for what i want, i'll keep them. I have emailed the company, will let you know if/what they answerI can't find any actual 'instructions', but he Heschen blurb about this too says:
Yep, tried that and seemed good. I just worry a bit. I asked the Spark to who i sent to verify if a cross/link bond was required. He said its better than he would have done!Yes, try it if you can't pull the lug off its as good as its gonna get
I worked for Vickers Armstrong in the 70s, crimping tools were calibrated then as were torque wrenchesWorking for GEC large steam turbines, our crimp pliers had to be calibrated, not seen it done with any other firm, but also the crimp had to be from one company, so in the main we do a test with over centre crimp pliers to see what jaw is required.
Lidi best look good, but as to selecting which jaw once the supplied crimps run out, it is really trail and error. But even with this cheap set, the jaws are marked.
Yes, pretty odd in comarison with what I'mused to seeing. This pic perhaps gives a sligttly clearer idea of what is going on - and it looks as if it's the 4-6mm² one (ratherthan the 8-10mm² one) which is 'the odd man out'! ...Yes, i thought that too. Not very clear imo.
It wasn’t too bad tbh, once I’d initially figured it out and got the crimp to stay put. They feel decent, but I value your input and it was actually your video that inspired me to get some4 holes, the markings are not all in the same location relative to the holes.
View attachment 416344It's a rather nasty piece anyway, and good luck crimping 10mm² with that and not incurring some kind of hand injury.