Well it tells us some things
5.7 Influence of residual current devices (RCDs)
Plug‑in solar shall comply with the requirements relating to DC residual current components in accordance with BS EN 62109‑1, Clause 7.3.8.
The device shall be designed such that it does not adversely affect the operation of upstream residual current devices.
Not sure how that will be done?
800 VA maximum export (3.5 amps) and 2000 watt maximum panel size.
Non-rewireable moulded plug fitted with a BS 1362 fuse not exceeding 5A; half-insulated pins.
No battery permitted.
G98 will be required. Likely will not be paid for export, only quick scan through the documents.
Where the consumer unit does not use modern protective devices, is not clearly labelled, or is of unknown condition, users shall be advised to seek inspection and assessment by a qualified electrician before installing the product.
If the electrical installation is using older fuse protection and does not incorporate RCBOs, the installation shall be checked and, where necessary, upgraded by a professional electrician;
So it would seem only true plug in solar if the consumer unit has Type A RCBOs otherwise an electrician required, but we have already shown not all Type A RCBOs are bidirectional, efixx seem to think it does not require bidirectional, but in the main we still have the same question, how to ensure the RCBO is bidirectional?
It also seems to say an amendment to BS7671 will be required, but the last one has still not come into force yet.
The bit I can't understand, if plug and play, how will the G98 work as the device is moved from property to property? It seems to be saying needs an electric meter which can measure in ½ hour slots, so also will need a smart meter to be able to use it.
However, only scanned through the document quickly, I may have missed something. As to the panels, with no battery, in my home around 300 watt would be the limit as far as self consumption, although I do use over that at times, the time it is used for is short, as without a battery the whole solar array can only really help when just covering back-ground use.
I also note the requirement to be type tested, so any units already sold will still be illegal to use.